Name this device | Page 2 | on ElectriciansForums

Discuss Name this device in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

Customer thinks it was installed in 1964 when the house was built!

[ElectriciansForums.net] Name this device

Thanks
 
If Murdoch is fitting a modern plastic CU with 30mA RCD’s is there a need for a front end E/L unit? Just use it as an isolator. Makes the job safer as there’s no playing about with live tails or dare I say interfering with the service head. (I’ll go and get the carbolic mouth wash now).
I’ve only done this once, I super glued the test button and painted it and the label black with the wife’s black nail polish. SHMBO wasn’t happy though.

If this is a TT installation with the typical Naff Ra values the UK seems to have adopted, then it's more than worthwhile having a front end 100mA S type RCD. I personally wouldn't like to totally rely on a single 30mA either side of the CU, they are still not the most reliable protective device out there!! lol!!
 
These were used as isolation switches by that world renowned bathroom company Dolphin

If you have ever opened up a original Dolphin shower,the sneaky lads at Dolphin design pinched these breakers to use as isolation switches for their showers

Would you believe they had a fancy looking piece of string linked to the elcb which was mounted side ways on and a glass front to hide the dirty deed
 
This is all before my time - a voltage-based RCD of sorts?

Were 'proper' RCD's too complicated/expensive to manufacture back then? Or not even invented?

In industry the core balance earth leakage relay has been around for donkey’s years. (Even before me!) They would be fitted to distribution CB’s.
How the voltage operated E/L unit came about I don’t know. But they were a bloody menace from day one! To get one to work correctly the gas and water services had to be isolated from the service pipe with a short length of polypropylene pipe. The only earth point in the installation would be via the voltage-sensing coil in the ELCB and then out to a spike.
It doesn’t take a lot imagination to find the problems.
Their redeeming feature was they were cheap(ish). My first house I fitted RCD’s to each of the Wylex boards. They cost damn near £150 35 years ago!
 
These were used as isolation switches by that world renowned bathroom company Dolphin

If you have ever opened up a original Dolphin shower,the sneaky lads at Dolphin design pinched these breakers to use as isolation switches for their showers

Would you believe they had a fancy looking piece of string linked to the elcb which was mounted side ways on and a glass front to hide the dirty deed

If you come across one again Des, have a closer look. The same chassis was used for MCCB’s. They all have 3 blind 2BA mountings holes on the front for panel use.

As for Dolphin I'll keep quiet. Bunch of &&& ^%$&* &$^*&(^% *&^
 
I believe that is a 3 phase earth leakage circuit breaker with overload protection. A kind of primitive RCBO with different leakage detection method, relying on a coil between real earth and installation earth.
Under the stickers there once would have been a plate that told you exactly what it is. See example of another one below.

I'm sure you already know that it needs taking out of service. And as the stickers read like a list of special locations with special requirements this one may need more than a little thought.

[ElectriciansForums.net] Name this device

[ElectriciansForums.net] Name this device


If you remove it, save it, as collectors might like it!
 
It looks like it.

Also something to have checked professionally to see if you have adequate protection for the installation as a whole since VOELCB have a number of issues, one being they are generally old and may not be tested (have you test tripped it?) and the other being that any additional earth bonding can make them ineffective at detecting a fault.

The other worrying sign is the apparent shuffling of phases!

It might be that device is now largely redundant if the distribution boards have RCDs in them providing the required level of protection, but I certainly would suggest it is checked. Do you have photos of the board(s) the device is feeding?
 
It looks like it.

Also something to have checked professionally to see if you have adequate protection for the installation as a whole since VOELCB have a number of issues, one being they are generally old and may not be tested (have you test tripped it?) and the other being that any additional earth bonding can make them ineffective at detecting a fault.

The other worrying sign is the apparent shuffling of phases!

It might be that device is now largely redundant if the distribution boards have RCDs in them providing the required level of protection, but I certainly would suggest it is checked. Do you have photos of the board(s) the device is feeding?
Thanks Tim & PC!!
The device feeds a 3P 63A switch fuse next door to it, then a long run of armoured cable to a modern 3P board, with RCBOs. Apparently the device is tripping once in a blue moon when there is a lot of load on. Sounds like from what timhoward says, it may be overload rather than leakage that trips it?. Sadly the plate is no longer there.
 
The device feeds a 3P 63A switch fuse next door to it, then a long run of armoured cable to a modern 3P board, with RCBOs. Apparently the device is tripping once in a blue moon when there is a lot of load on. Sounds like from what timhoward says, it may be overload rather than leakage that trips it?. Sadly the plate is no longer there.
It sounds like it, though of course enough accumulated leakage might trip a RCD-like device (though on 3P a lot of the would cancel so really it would be imbalance on leakage).

If this is a TT set up then the sub-main would need some sort of RCD protection as a L-E fault there would probably not take out any supply OCPD. As there is a switched-fuse for overload (I guess?) all that would be needed is a delay RCD. Also it probably falls in to the special locations where <= 300mA RCD for fire is required.

If it were my business I would look at replacing it with a 100mA or 300mA delay RCD in a suitable enclosure.
 
It could be overload tripping it. Or it could be a fault with a distribution cable. I'm afraid it really needs looking at.

These devices are often found where the earthing for an installation is a rod in the ground (known as TT), and the original job is turning things off safely if there's a fault. With this kind of earthing it's very important to have a device like this as not enough current will flow to operate the suppliers fuse under fault conditions.
Anything between the RCBO's and the origin are probably relying on this for fault protection, and even if it's working it really needs replacing with a modern RCD.
 
It sounds like it, though of course enough accumulated leakage might trip a RCD-like device (though on 3P a lot of the would cancel so really it would be imbalance on leakage).


If it were my business I would look at replacing it with a 100mA or 300mA delay RCD in a suitable enclosure.
Thanks PC! Yes, it's TT. I was thinking 300mA type S. So much hanging off it, 100mA could nuisance trip, even with everything on 30mA RBCOs. I think they left this in as they did not want to mess with the meter tails...
 
STD stands for Short Time Delay.
back in the 70's, with BT it was Subscriber Trunk Dialling.
now with the sawbones, it's Sexually Transmitted Disease.

take your pick ( or if your Irish, alternate with a shovel ) .
 
So even a decade old thread can be informative.

I see the labels on the thing mention tractor shed…. So, on a farm? Likely never been tested.
But also cafe? So an area open to public… let’s hope there’s rcd protection in there at least.
 
I believe that is a 3 phase earth leakage circuit breaker with overload protection. A kind of primitive RCBO with different leakage detection method, relying on a coil between real earth and installation earth.
Under the stickers there once would have been a plate that told you exactly what it is. See example of another one below.

I'm sure you already know that it needs taking out of service. And as the stickers read like a list of special locations with special requirements this one may need more than a little thought.

View attachment 94275
View attachment 94276

If you remove it, save it, as collectors might like it!

Disconnect the in/out earthing polls....and keep it to use it as an on load isolator...
As the contacts in it are capable of making/breaking full load rating...
 

Reply to Name this device in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
word of caution, the federal electric breakers are old bits of kit. I have known them sometimes to refuse to turn back on if they are tripped or...
Replies
7
Views
643
  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
305
  • Question
Well I suppose just a light across the pump would provide remote indication that the pump is running. However, that requires EVERY user to...
Replies
6
Views
562
  • Question
It is not a brand that I know, but on the appearance it would look like a good enough choice for most situations where you do not expect a direct...
Replies
7
Views
849
  • Question
pretty sure from memory they are indeed designed to work on both frequency's, Best check with Schneider but I think they will work on 60 HZ
Replies
4
Views
536

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks