I am unable to take global IR readings on a 3 phase consumer unit, i have disconnected the neutral but when i try to measure the meter never settles and eventually times out.
i have tried 2 meter/s with same results
 
Sounds like some power is present even when isolated.

Have you looked to see what sort of volts L+N - E has when isolated? You might also need to put in a small load (1k resistor, or maybe a basic voltage tester in parallel to meter) so you are not seeing low current "phantom" voltages.
 
it seems almost random, put a clamp round the earth found 100mA leakage from lighting circuit,(14 double D fittings
CPCs often have strange currents due to whatever route power from TN-C-S systems is finding back to the substation, etc.

Clamping L&N to get actual leakage is far more useful!
 
Usually i would clamp the L-N but this is 3 phase so that’s quite tricky, the 100mA is only present when the lighting circuit is on ,when turned off it drops to 2 mA ,i have also clamped the cpc from the lighting circuit which confirms 99mA back down it!
 
Unless I'm missing something here or being slow (always an option!!) if you're wanting global IR then just gang the lines together? As for the leakage, 100mA on a large LED lighting circuit doesn't seem implausible, although if that IS the case then it's been poorly designed.
 
Usually i would clamp the L-N but this is 3 phase so that’s quite tricky, the 100mA is only present when the lighting circuit is on ,when turned off it drops to 2 mA ,i have also clamped the cpc from the lighting circuit which confirms 99mA back down it!
OK, that is sounding like a N-E fault somewhere!
 
Finally found the problem , this along with a loose cpc made for a rather dangerous situation on exposed class 1 head height light fittings.

thanks for all the suggestions
 

Attachments

  • [ElectriciansForums.net] Strange IR readings on 3 phase board
    A0C9F783-E010-434E-AF26-9F93F975C3FF.jpeg
    150.8 KB · Views: 12
  • [ElectriciansForums.net] Strange IR readings on 3 phase board
    75D7D4DC-F332-4D75-A50E-B9058F96C19D.jpeg
    124 KB · Views: 12

Reply to Strange IR readings on 3 phase board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
172
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
542
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
489

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
364
Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
554

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top