As part of unlooping the DNO has installed 3-phase domestic supply. My supplier has installed a 3 phase meter as well.
I believe I now need to have a 3 phase distribution board installed?

Can any of you guys know how long this would take at all? I do not know what hardware is required?
It would be prudent to install a new CU as well, as the current one is 30 years old.
Thank you for your consideration.
 
Last edited:
You don't need to have a 3 phase D.B installed, you can still just have a new single phase one, unless you have sufficient load / circuits to justify it.

I believe the DNOs installing 3 phase supplies are / will be the standard in future.
 
With what fuse rating per phase? If it's only 25A, keeping the max power to about the same as before, this will cause its own problems.
I'm more concerned about all the destroyed neutrals!! At least at the moment the DNO's can have limited control over phase balancing, install 3ph all over the place and you've lost that control. Add to that the increasing issues with SMP's and it's a recipe for disaster. There's also the challenge of limiting the pfc in a domestic setting even if the incoming fuse is only say 60A it's not hard to go into the 6+ kA bracket.
 
Hello,
As part of unlooping the DNO has installed 3-phase domestic supply. My supplier has installed a 3 phase meter as well.
I believe I now need to have a 3 phase distribution board installed?

Can any of you guys know how long this would take at all? I do not know what hardware is required?
It would be prudent to install a new CU as well, as the current one is 30 years old.
Thank you for your consideration.
If you are intending to replace the consumer unit anyway (good idea) then you may as well install a 3 phase one as the cost should not be much different.
it will give you a bit more flexibility especially if at some point in the future a car charger is installed.
i.e a 3 phase charger draws 16A per phase and charges at up to 12Kw
a single phase charger draws 32A on a single phase and charges at up to 7.5Kw
 
Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board in. I would like to have TPN into my house to be honest, would be great for the workshop..
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
3-phase installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Bertybert,
Last reply from
Bluetit,
Replies
5
Views
602

Advert

TrueNAS JBOD Storage Server

Back
Top