Hi
A customer has a new farm shed going up supplied also from a new 100KVA transformer right outside. The supply spec states that PSCF could be as high a 25.9KA on the quote he has been given. The usual kit I use is rated at 10KA. There terms also state that the connection by DNO will not be carried out until the install is in.
Is this a normal reading for close proximity of Transformer straight off the HV?
Are these 'anticipated' readings likely to be reflected in real life, about 20m from transformer?
If i provide tails to an isolator and means of earth marshalling and connections, are they likely to connect - i can then at least test the actual PSCF current before purchasing distribution kit.
If PSCF current is that high, anyone any guidence on manufactures of 26KA rated devises we can use? I normally use MCG or Hager. Only looking at standard farming type equipment, ring mains corn dryer, lighting.
Thanks.
John
A customer has a new farm shed going up supplied also from a new 100KVA transformer right outside. The supply spec states that PSCF could be as high a 25.9KA on the quote he has been given. The usual kit I use is rated at 10KA. There terms also state that the connection by DNO will not be carried out until the install is in.
Is this a normal reading for close proximity of Transformer straight off the HV?
Are these 'anticipated' readings likely to be reflected in real life, about 20m from transformer?
If i provide tails to an isolator and means of earth marshalling and connections, are they likely to connect - i can then at least test the actual PSCF current before purchasing distribution kit.
If PSCF current is that high, anyone any guidence on manufactures of 26KA rated devises we can use? I normally use MCG or Hager. Only looking at standard farming type equipment, ring mains corn dryer, lighting.
Thanks.
John