100kVA is 150A 3-phase, so I'm guessing 160A fuses. You won't find MCBs above 15kA in most cases, and MCCB options cost a lot.

Depending on what loads have to be supported you might want to look at two 80A fused-switches each feeding normal 125A or similar TPN boards with MCB/RCBO in them. The fuses will have total selectivity with the supply fuse, and for faults near the ends of final circuits probably selectivity MCB/fuse, but that would need checking if short cables, etc.
 

Reply to Proposed Connection for new build states prospective will be as high as 25.9KA in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top