Hi, I have installed a faac c721 with 4 Photocells and everything we connect the transformer it trips the power in the house. We have tested and we get 250v but cannot understand why it keeps shorting the circuit. The c721 is just sat on driveway can't get around it. Has anyone noticed problems with this before - the transformer could just be a smoke screen it's brand new only a couple of weeks old. Faac have said send it back for testing but that's a nightmare with all the blockwork settled back in. I have the nylon racking off also. Any help would be grateful.
[ElectriciansForums.net] Faac c721 shorting power on mains
 
Is the gate motor unit connected to an existing circuit or a new one?
Is there anything else inside or outside that is also connected to that circuit?
Either way can you identify which MCB on the consumer unit that circuit is.
 
Have you tried connecting the transformer alone (no secondary connections) ?

What size transformer is it?

Might help to post a picture of the transformer and its connections.

As asked above what is the ir reading L+n to earth?
 
Hi, it was all 3 on the first test and then 1 RCD and then 2 RCDs on another test. We noticed it was when the transformer was connected that's when it tripped. Plugging everything else in one by one and then pop when the transformer was plugged in.
Your reply seems to suggest that all your "testing" is purely a plug in and wait for the RCD to trip, have you got the necessary test equipment to carry out dead testing and subsquently the live testing
Your profile indicates you are a trainee electrician are you working with someone who is qualified on this job
 
Have you tried connecting the transformer alone (no secondary connections) ?

What size transformer is it?

Might help to post a picture of the transformer and its connections.

As asked above what is the ir reading L+n to earth?

Is the gate motor unit connected to an existing circuit or a new one?
Is there anything else inside or outside that is also connected to that circuit?
Either way can you identify which MCB on the consumer unit that circuit is.
Hi, thanks we have a fuse switch spare and a safety isolator switch connected to the circuit going from the one right of number 5 on the fuse board. Nothing else is connected to number 5 on the fuse board.
 

Attachments

  • [ElectriciansForums.net] Faac c721 shorting power on mains
    20220511_075210_2.jpg
    259.2 KB · Views: 24
  • [ElectriciansForums.net] Faac c721 shorting power on mains
    20220309_104408 (1).jpg
    1 MB · Views: 34
  • [ElectriciansForums.net] Faac c721 shorting power on mains
    20220309_104340 (1).jpg
    359.4 KB · Views: 43
Your reply seems to suggest that all your "testing" is purely a plug in and wait for the RCD to trip, have you got the necessary test equipment to carry out dead testing and subsquently the live testing
Your profile indicates you are a trainee electrician are you working with someone who is qualified on this job
Hi, yes 100% i am no expert but this was carried out by an electrician and has left it all unplugged - just trying to see for some help. I deal more in access control configuration so my job comes in when the unit is connected and programming it :)
 
Hi, thanks we have a fuse switch spare and a safety isolator switch connected to the circuit going from the one right of number 5 on the fuse board. Nothing else is connected to number 5 on the fuse board.

It could be a fault with the secondary wiring - can't tell unless you try it without the secondary connected

It could be transformer inrush, can't tell unless we know the size of the transformer.

It could be the transformer's connected incorrectly, can't tell unless we see a photo of the Connections

It could be an internal fault within the transformer, can't tell without the ir readings

A number of people have asked a few leading questions in order to narrow the issue down, without any response without the information we will not be able to help you.

We can all have a multitude of informed guesses as to the issue, but are unable to narrow it down without the questions being answered.
 

Reply to Faac c721 shorting power on mains in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
181
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
556
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top