Hi, I have installed a faac c721 with 4 Photocells and everything we connect the transformer it trips the power in the house. We have tested and we get 250v but cannot understand why it keeps shorting the circuit. The c721 is just sat on driveway can't get around it. Has anyone noticed problems with this before - the transformer could just be a smoke screen it's brand new only a couple of weeks old. Faac have said send it back for testing but that's a nightmare with all the blockwork settled back in. I have the nylon racking off also. Any help would be grateful.
[ElectriciansForums.net] Faac c721 shorting power on mains
 
Let us know how you get on
Thanks got there in the end with an electrician and now we have power to the gate ready for automation.

I asked what was wrong and here it is

Live and neutral crossed on the rcd (one connected one side, one connected the other side of the consumer unit)

And mcb too small (6amp should've been more than a 12 amp)
 
Last edited:
With this one - 👍
I think fitting an RCBO for the gate circuit would have been a better and more prudent option, kitchen socket circuit and a gate circuit on the same RCD could be problematic if the RCD trips, seen it before family go away on holiday and come back to a freezer full of defrosted food because the gate circuit developed a fault
 

Reply to Faac c721 shorting power on mains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Youre in the same boat as me. I was previously with niceic and later on, napit. No issues. I didn't bother finishing my nvq3 as in 2010 during the...
Replies
7
Views
3K
  • Question
Post in thread 'Domestic - Voltage fluctuations on a 1000VA 600W UPS with 40% load when on battery' by kuddoo has been reported by kuddoo. Reason...
Replies
0
Views
94
R
Yeah getting a part p spark is fine but just make sure he relabels the consumer unit with the PV stickers. He also needs to be aware of how to...
Replies
29
Views
4K
iconnect
I
D
The only cabling that's affected is the cabling n this circuit which is new blue and brown cable so not that old at all. The rest f the house...
Replies
10
Views
4K
DonaldJ
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks