Start with the spec of the lights, work out the total power (or more correctly, current) is needed. Assuming it's LED then it'll be fairly low.
You can now have a stab at picking a cable size - though in practice the answer will almost certainly be "the minimum allowed by the regs" (it's in there, you find it
).
You can then work out volt drop and check that it's within limits (again, it's in the book) - if not, then you'd have to up the cable size, find another way of improving things, or decide whether the excess is an acceptable deviation from the standard.
Pick an upstream overcurrent protection type and rating, work out if it's compatible with the fault impedance. Consider the characteristics of the loads when selecting the OCP - for example, if you had a big space with loads of flouro tubes, there's scope for significant inrush current. Most types of light have some sort of inrush - some more than others.
You'll also have to consider the CCC of the cable taking into account the installation method.
If necessary, you may need to iterate. E.g., if you have a larger than typical Ze or Zs, or a long circuit length, you might find that the overall fault impedance isn't acceptable for the OCP you've chosen. So then you need to consider what options there are to fix that.
So there's the steps you should already know - off you go, find the information, and do the calcs. Voila, circuit designed.