Hi guys.
Been to look at a job today to replace old wylex board.
Feed to unit seen in pictures fed from garage. It 16mm twin and earth.
I’m unable to access cables entering board so would struggle to replace with swa.

[ElectriciansForums.net] Any suggestions for feed to consumer unit?
[ElectriciansForums.net] Any suggestions for feed to consumer unit?
 
Looks from the pictures thats at some stage someone ripped the original cable out from its buckle clips and added the rcd on that bit of wood

I would like to re-do the submain in swa if possible but if not then you could put a small garage board where the original switch was and put the submain on its own rcbo

But you then have the issue of a front loaded rcd
 
Looks from the pictures thats at some stage someone ripped the original cable out from its buckle clips and added the rcd on that bit of wood

I would like to re-do the submain in swa if possible but if not then you could put a small garage board where the original switch was and put the submain on its own rcbo

But you then have the issue of a front loaded rcd
Thanks for the reply.
I was thinking remove the upside down rcbo in picture. Replace with jb, separate pme to new rcbo consumer unit
 
Looks from the pictures thats at some stage someone ripped the original cable out from its buckle clips and added the rcd on that bit of wood

I would like to re-do the submain in swa if possible but if not then you could put a small garage board where the original switch was and put the submain on its own rcbo

But you then have the issue of a front loaded rcd
I give up with predictive text!!!!
M.E.T!!!!!!!!!!
 
You can use the T&E and pull in a new 16mm main earth ( I would still also connect the cps from the T&E aswell )
But you must remember that the submain needs to be front RCD protected IF its runs through the fabric of the building.
We had something similar in our old house and the RCD was in the outhouse which meant if the RCD tripped I would need to venture outside to re-set it
 
You can use the T&E and pull in a new 16mm main earth ( I would still also connect the cps from the T&E aswell )
But you must remember that the submain needs to be front RCD protected IF its runs through the fabric of the building.
We had something similar in our old house and the RCD was in the outhouse which meant if the RCD tripped I would need to venture outside to re-set it
Good shout. I could mount one tidier in box. I’d expect nuisance trips but would explain to customer.
 
Unfortunately not. It’s a mid terrace.
I think the house was built around the cable!!! Lol!
Cable would have been pulled in before the floors and ceilings were put in. Your saving grace is in old houses like these you have floor boards where are much MUCH easier top pop up than horrible horrible chip board which is the devils flooring
 

Reply to Any suggestions for feed to consumer unit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Does it really actually need earth sleeving inside the tube? I know it feels a bit bodgy but what's going to happen and isn't an unbroken...
Replies
9
Views
527
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
531
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
1K
Sounds more positive.
Replies
8
Views
464
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks