7kw electric shower - 4mm2 too risky? | on ElectriciansForums
Discuss 7kw electric shower - 4mm2 too risky? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yonny24
Uruguay
Hi all,
Been a while since I've posted - got a new project to install a small 7kw electric shower.
The shower will be about 7 metres from the main fusebox on the upper floor.
There seems to be a lot of debate about 4mm2 or 6mm2 wiring.
Due to the diameter of the wall conduits, I doubt very much I'll be able to fit 2 x 6mm2 cables in there so I was thinking of 4mm2.
Obviously, I want to keep it all safe. Would I get away with 4mm2?
If I used 4mm2 would I need to keep it outside of the wall in the air?
The house has electric underfloor heating and all is cabled with 4mm2 also between the lower and upper fuseboxes (short distance about 1.5 metres).
We rarely use the underfloor heating on the upper floor - only the small bathrooms rated at 300w.
Both floors have the usual master circuit breakers, RCD's etc.
The house is installed with a 'three phase 2 wire corner grounded delta' btw
Thanks!
If you want us to double check your cable calculations, just post them here.
it would be unusual for a diy person to install a shower because of the building control notification and certification can be troublesome.
do you have an electrician that you have used before and can trust or are you looking for one?
Nobody has electric showers here in Uruguay. I brought it from UK.
I have zero trust in electricians here (especially with an electric shower that they most probably have never seen before), many times I've had to fix and improve electrical installations done by previous owners using so-called qualified electricians!
I research well and make sure everything is installed correctly first.
The model is a Triton Seville
I understand the mains voltage in Uruguay is 220V.
The Triton Seville spec shows the 7.5kW is at 240V
By my calculations, and assuming it is a resistive (7.67 ohm equiv.) load, the current it will take on 220V is 28.7A
I think two 4mm singles in conduit would be OK, perhaps others here can comment. Don't know what your regulations require in Uruguay
[ElectriciansForums.net] 7kw electric shower - 4mm2 too risky?
I wouldn't have any issues wiring such shower in 4mm at such a short cable run on a 32amp device
Shower will only being pulling load for 4-5 minutes for a normal persons shower
In a perfect world we would all use 6mm but if space is tight in an existing conduit system I myself would just use 4mm
That's good to know thanks.
Makes the installation 100 times easier.
First few runs I'll keep an eye on the temp of the cables though
Would someone cover equipotential bonding please and nearby double pole pull cord isolating switch with neon or on/off indicator .
Make sure the 30mA RCD and the 32A typeB mcb are double pole. If you can it would be neater to use a combined RCD and MCB called an RCBO.
I would be very surprised if the cables get warm to the touch after a normal length shower (3-4 minutes)
Cables only tend to get very hot to touch after a good while of constant overload
Connect across lines with lowest loading.
What is the size of the main fuses/circuit breakers?
Can you see thick earth conductors connecting your main earth terminal to incoming gas and water pipes? Is pipework within home plastic or metal or a mixture of both.
Check there is a thick earth conductor between main earth terminal and to an earth electrode.
Photos are helpful.
Photos are helpful.
Hi Marconi,
No there aren't any connections to pipes. Al the water pipes are modern green thermofusion plastic-type and we do not have gas pipes.
I will need to install an earth wire through the conduit from the bathroom to the fusebox though. 4mm2 also?
MCB and RCD:
Is this an RCBO? It says in Spanish translated - 'circuit breaker - RCD'.
No. That is an rcd and a double pole one rated at 16A. I will send info on an rcbo once we decide on what is practical to fit.
yes you will need to run a 4mm2 circuit protection conductor from consumer unit to the shower.
The sassin is rated at 40A. Please take a picture of the front of it when turned off so I can confirm what poles it switches.
the Schneider rcd to the right of the power meter is only rated for 25A so you cannot feed the shower via it.
please carefully take the cover off the consumer unit, keep you fingers and any tools out if it and then take a picture of inside it so I can confirm how many lines are present.
I seem to remember without going back to our previous posts that you have another ‘fuse box’ at the point where the electricity company provides your supply. If my memory is correct please take a photo of it so I can see the fuse/mcb ratings.
Also take a picture showing all the outgoing ways of the cream consumer unit and label what they are for.
And I note that all water pipes into and in your house are plastic ones.
enough for now.
enough for now.
Thanks will get some new photos taken later. I looked at my old post with all the photos but they are not accessible anymore. Possibly been erased?
Our house does have a fairly heavy-duty power supply coming in- rated to supply 15,000w (3 -phase) at least for the underfloor heating in 10 rooms, plus all the appliances etc (we only use 2 of these 10 floor heating zones for 2 hours a day)
Assuming 15kW is the figure then over ‘3 phases’ (actually two lines and a neutral) that is 5KW a ‘phase’ which is not enough to run a 7.2KW shower which is single phase and must be connected across L1-N or L2-N or L1-L2. This why we need to check carefully your supply is adequate.
[ElectriciansForums.net] 7kw electric shower - 4mm2 too risky?[ElectriciansForums.net] 7kw electric shower - 4mm2 too risky?
The 1st photo shows the main consumer box with the exterior cable coming in with the thick red, white and brown cables.
Then the 3 white cables shown with the arrow are the ones that go upstairs to the upper floor consumer box.
The 2nd photo shows the main MCB with the 3 white cables coming in from the lower floor main consumer box. 3 of these split off into a separate circuit for the floor heating.
I guess the shower RCBO(or RCB and MCB) 32A would be fed from the thick white cables that come directly from downstairs
BUT I see the main circuit breaker downstairs is a C63 isn't it (which would support the 15000W)?
The shower manual states if the house does not have an 80A or more main switch then a consumer unit serving just the shower would be required.
Not sure why the manual states 80A. Is this a UK requirement perhaps?
Forgive the 'questions, questions, questions' but I want to be sure about things.
What size are the conductors in the incoming supply cable with the red, white and brown conductors going to the input to the C63A below?
What size are the three white conductors leaving the C63A and heading to the C40A upstairs?
Is there any space inside the upper consumer unit for either an rcd and mcb or an rcbo? If not is there space 'somewhere' very adjacent for a separate enclosure containing these?
Which of the pairings L1-N, L2-N, L1-L2 has the most spare capacity ie has the lowest kW of connected loads.
What does the C16 to the left of the C63A supply? Is it connected across L1 and L2 ie red and brown/blue
If I remember correctly L1 and L2 are red and blue and N is white (except for the three whites between the C63A and C40A.
Have you found your home's earth electrode?
And should to get the picture straight in my mind, apart from C16 below, the C63 only feeds the C40 above? I ask because it looks like may be some reds go into the bottom left of the C63 - see blue arrow in my attachment.
  • [ElectriciansForums.net] 7kw electric shower - 4mm2 too risky?
Special locations.
In the UK we have strict regulations for electrical equipment and its wiring in special locations such as wet rooms, bathrooms and showers. I have attached a short video which should help you understand what can and cannot go where. I do not know what is expected in Uruguay. I assume you can find out. You should plan your shower installation carefully which includes positioning and IP rating of lighting, extractor fans, switches and even the running and protection of cables. All cables passing through a bathroom, wet room or shower must be rcd protected.
Will you have underfloor electric heating near the shower?
For any detailed questions on this topic I ask you to rely on the practicing electricians of the EF. I am only introducing you to the requirements.
Many thanks all.
Will take me a bit of time to make notes to the questions, winter school holidays now so weekends are busy with the kids/family. Also got a big repair to do on our flat roof which takes priority.
First job though is to upgrade the home's earth electrode point outside. These ones here seem to be widely used with an inspection hole. 1.5 metre copper.
leave existing rod in, clean connection/s if requred. add another rod 2m away, parallel. up and get a reading.
Also the current grounding rod is very far from the main consumer box in the front garden 6 metres also from the house. Probably better to place a new one in the backyard which is just 2 meters from the main box in the kitchen.
That's almost certainly an rcbo.It says C16.If it was an rcd it would say "16 amps".
My electric shower is wired in 4mm (its a rented house).Its a T90 si, approx 1 kw larger than yours.The 4mm made me a little nervous at first and I checked the cable regularly for the first year or 2.The supply cable is in mint condition.I dont check it any more.
Before installing another electrode I would check first what kind of supply system you have (TNCS or TT)
I take it you have no girlfriend/wife or any daughters then?
To be fair in my own home or on holiday I'm in shower a damn sight longer than 3 minutes too.
My misses will spend 15-20 mins and 12 Yr old so the same or more if he has his music playing 🤣
Currently we have those Spanish style water heaters (calefon). 1500w element in a 60 ltr tank that hangs on the wall. So inefficient as when you are using the hot water cold water enters the tank at the same time.
As an expat I miss the power showers, no limits and instant hot water.
Wife is always asking is there hot water? When we moved I brought the Triton shower with us in the container but never installed it.
Top guy Telectrix who knows his onions - ask him about zones etcetera in bathrooms.
It is a good idea to have some small holes in the cover over the earth rod so that rain water can pass through and keep the ground underneath moist. This is what I have seen in rural southern Italy where my aunt lives which is hot and dry for long period with occasional rain.
To re-iterate - you require an additional electrode close to the consumer unit as Telectrix advised. Use 6 or 10mm2 insulated green yellow cable between it and CU. Don't disconnect the present one further away. You will connect the new electrode to the earth bar in the CU. Two metres away or thereabouts is fine.
Reply to 7kw electric shower - 4mm2 too risky? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
T
Electric underfloor heating onto concrete floor. I have a customer who lives in a 200 year old property. The lounge floor he wants tiled which is...
Teign Tiler
T
G
Waterproofing options for new shower room Hi, A newcomer here and thank you to anyone with the patience to read my drivel. I am renovating an...
Givey Tago
G
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
S
Unidentified noise in party wall Hi 🙂 Please can anyone help to identify this noise in the wall between me and my neighbour? Complicated but will...
shrewmouse
S
What type of car have you got/ordered ? I use a portable charger, can charge as low as 6 amps and the car's maximum is 26 amps. I have a number of...