Thank you. I will study tomorrow morning. It is 1830 here now.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 7kw electric shower - 4mm2 too risky? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Also the current grounding rod is very far from the main consumer box in the front garden 6 metres also from the house. Probably better to place a new one in the backyard which is just 2 meters from the main box in the kitchen.leave existing rod in, clean connection/s if requred. add another rod 2m away, parallel. up and get a reading.
Is this an RCBO? It says in Spanish translated - 'circuit breaker - RCD'.
Thanks
View attachment 99255
I take it you have no girlfriend/wife or any daughters then?I would be very surprised if the cables get warm to the touch after a normal length shower (3-4 minutes)
Cables only tend to get very hot to touch after a good while of constant overload
My misses will spend 15-20 mins and 12 Yr old so the same or more if he has his music playingI take it you have no girlfriend/wife or any daughters then?
To be fair in my own home or on holiday I'm in shower a damn sight longer than 3 minutes too.
Forgive the 'questions, questions, questions' but I want to be sure about things.
What size are the conductors in the incoming supply cable with the red, white and brown conductors going to the input to the C63A below?
What size are the three white conductors leaving the C63A and heading to the C40A upstairs?
Is there any space inside the upper consumer unit for either an rcd and mcb or an rcbo? If not is there space 'somewhere' very adjacent for a separate enclosure containing these?
Which of the pairings L1-N, L2-N, L1-L2 has the most spare capacity ie has the lowest kW of connected loads.
What does the C16 to the left of the C63A supply? Is it connected across L1 and L2 ie red and brown/blue
If I remember correctly L1 and L2 are red and blue and N is white (except for the three whites between the C63A and C40A.
Have you found your home's earth electrode?
And should to get the picture straight in my mind, apart from C16 below, the C63 only feeds the C40 above? I ask because it looks like may be some reds go into the bottom left of the C63 - see blue arrow in my attachment.
Many thanks Marconi.I have been re-reading the discussion we had on your uf. I found this post by you:
Here we have the ground floor contactors. 4 thermostats (cheap copies of Honeywell and do not work well at all). Installing a central digital thermostat that will send a signal to the sonoff switch in the fuse box.
Living room
Dining room
Breakfast room and kitchen (2 zones).
Living room about 11-12m2 consumes about 2000 kwh.
Dining room a little less and kitchen/breakfast about 1800 combined.
No more than 6000 kwh. (230v)
Could you confirm that you are reporting the power in kW of the ufh in these rooms and not their power consumption in kWh.
If you are reporting power in kW can you tell me how the power in spread over the three lines? I cannot open up any earlier diagrams you produced. Is each room’s ufh fed by it’s own breaker, a 20A I seem to remember? I vaguely remember we installed two power meters and after these the ufh was equally split over the lines.
Are these rooms ufh all supplied from the same board (via the C40breaker)?
Do you have an electric oven and an electric hob? If yes what lines do they connect to And via what size breakers. To which board does the oven and hob connect to? Can you see the power of these appliances on their spec plates?
Let me tell you that what I want to confirm is the shower can safely be supplied after the C40 breaker between L1 and N or L2 and N, the pair selected having the capacity to provide 28A for the shower and with 12A remaining for everything else which may by drawing significant current While the shower is on. So shower, oven, hob and a third of the ufh on one L-N pair would be a problem Since 28 + 10 + 20 + 10 = 68A Which would trip the C40. whereas shower plus 1/3 of ufh would be 28 + 10 = 38A which would not trip C40.
Suministro Trifásico (potencia en kW) |
---|
6, 8, 10, 12 * |
15 * |
20 * |
25 * |
30 * |
35 * |
40 * |
41 a 50 * |
Reply to 7kw electric shower - 4mm2 too risky? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net