I’ve got my P16th edition papers in 2006 so not a total beginner (I’m plumber as my trade tbh) but this pull chord bathroom light is not working and if trips the consumer unit .

Basically the old switch broke so I took a photo of the wiring before fitting a new light.

And it doesn’t work.

The brown an red wires are live and the two connect together are live too. I test them with this blue pen tester .

I’m gonna include photos of everything so any help be great thx
 
TL;DR
I know what I’m doing but basically I’ve no idea what to do here. I’ve just copied what was there before

Attachments

  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    362.2 KB · Views: 39
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    0A51F626-B8EB-43C0-A335-3A621B71B4C9.jpeg
    350.7 KB · Views: 33
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    4130C53C-8A03-426D-8263-9CE4ACF0C088.jpeg
    408.8 KB · Views: 31
  • IMG_7254.MOV
    4.6 MB
  • IMG_7255.MOV
    14.6 MB
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    4718D26D-FFEC-473F-A58D-2F3949F94275.jpeg
    408.8 KB · Views: 32
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    1A3B9300-6B5C-477B-ABED-6DAC4415246E.jpeg
    350.7 KB · Views: 35
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    5F1F3656-4B2C-463A-BB7D-6379D6B21998.jpeg
    419.9 KB · Views: 35
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    690.5 KB · Views: 33
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    353.3 KB · Views: 27
What I would expect at the pull cord position is that the switch would have been between the red and brown wires, the two earth cores properly sleeved and connected to the switch earth terminal (if there is one), and the black and blue wires connected together by a wago or terminal block isolated from everything else.
Then at the light fitting, traditional connections of L, N and E.
Is this how you have tried wiring it?
Your old switch is two way, but it looks like only the two screws on the left side (third photo) have been used- I'm assuming there aren't enough wires for a two way circuit. Is there another switch for this circuit?

Tidying up of wire lengths and sleeving needed!

The above rather rashly assumes wire colours have been used for their traditional purposes.

Also be wary of quirks of pen tester.
 
Last edited:
What I would expect at the pull cord position is that the switch would have been between the red and brown wires, the two earth cores properly sleeved and connected to the switch earth terminal (if there is one), and the black and blue wires connected together by a wago or terminal block isolated from everything else.
Then at the light fitting, traditional connections of L, N and E.
Is this how you have tried wiring it?

Tidying up of wire lengths and sleeving needed!

The above rather rashly assumes wire colours have been used for their traditional purposes.

Be wary of quirks of pen tester.
Thanks for replying so fast but that’s what I did the red in common, brown L1, then the Earths to to E box (u can see where it’s been scorched)

I’ve got a traditional multi meter and so which wires would I test with Red and Black pls?

I thought the pen test was a bit crap when the Earth cable would beep the pen after a few secs!

Thsnks in. Advance (if u reply)….!
 
Thanks for replying so fast but that’s what I did the red in common, brown L1, then the Earths to to E box (u can see where it’s been scorched)

I’ve got a traditional multi meter and so which wires would I test with Red and Black pls?

I thought the pen test was a bit crap when the Earth cable would beep the pen after a few secs!

Thsnks in. Advance (if u reply)….!
In your movie the black wire looks nicked - did it get trapped somehow? That bit needs cutting off if you have enough cable length.
Firstly what trips in the consumer unit - MCB or RCD or what?

What are the wire colours at the light fitting? (black/red, or blue/brown) - I mean the wire coming out of the ceiling.
If the new fitting is up, with power off you could disconnect switch and check for any short circuit (between L-E or L-N etc)

Sounds like your earth core may not be connected, or with all this bare conductor about, has got trapped and connected to something it shouldn't!
 
Last edited:
In your movie the black wire looks nicked - did it get trapped somehow? That bit needs cutting off if you have enough cable length.
Firstly what trips in the consumer unit - MCB or RCD or what?

What are the wire colours at the light fitting? (black/red, or blue/brown) - I mean the wire coming out of the ceiling.
If the new fitting is up, with power off you could disconnect switch and check for any short circuit (between L-E or L-N etc)

Sounds like your earth core may not be connected, or with all this bare conductor about, has got trapped and connected to something it shouldn't!
I’ll take some more photos and post them now
 
more photos
The trip switch is first one on the left
 

Attachments

  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    754A5946-9652-4825-BCDA-43586D96EBDB.jpeg
    335.2 KB · Views: 22
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    1D5A36DA-B2E6-46AF-8FE1-A2BFA965317E.jpeg
    348.3 KB · Views: 25
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    810DD0F0-ECD1-4B3E-AFC5-302D81459905.jpeg
    227 KB · Views: 22
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    3FDA34D8-9667-4184-811F-9967BAE6FE00.jpeg
    372.5 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    C10247E8-05C1-43DC-8E72-93C4A6A4CD4D.jpeg
    311.1 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    B5AF8C51-D4BF-4FDB-B6A1-30F8A824BDDE.jpeg
    388.2 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    03E319AF-B04F-45ED-9578-6F8AE1DAF593.jpeg
    372.5 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    49286AF6-E2A3-4BA8-84CB-84550E631299.jpeg
    311.1 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    DBF5529B-FC85-4ABB-8B45-66C28E63AEC4.jpeg
    227 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    6F9CCFF6-0A7D-4FE5-BC0B-07DA78749D73.jpeg
    345.9 KB · Views: 19
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    4784BC13-8DBF-48CB-AAA8-C25225F40637.jpeg
    324.2 KB · Views: 27
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
 
Last edited:
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
OK
So I'm sorry but I don't understand what I'm looking at in the multitude of photo's.
The last ceiling fitting in your first post, is not the same as the last photo in the second post of photos (post #6)?
Do you have two seperate ceiling fittings?
The last photo in the #6 post shows two red wires in the ceiling rose. where has that second red wire come from and go to?
I don't see two red wires in any of the other photo's!
Tell me the setup Please!

So it's the MCB on the left of the CU that trips, not the RCB on the very right?
I guess that means you have some sort of short circuit between L & N on this circuit
I’ve pulled the wires down and cut little bit grey sheathing off.

The other pictures are the light fittings where the wires connect to the lights themselves.

Then a picture of the consumer unit

Hope this helps!
 
I’ve pulled the wires down and cut little bit grey sheathing off.

The other pictures are the light fittings where the wires connect to the lights themselves.

Then a picture of the consumer unit

Hope this helps!
Just to clarify - there are two light fittings as well as the switch?
Have you already rewired the ceiling rose shown in the last photo (I mean the photo with the close up of the metal bar), with the two red wires in it?
Presumably you have two red, two black, and two earth feeding that light?
 
Last edited:
Just to clarify - there are two light fittings as well as the switch?
Have you already rewired the ceiling rose shown in the last photo (I mean the photo with the close up of the metal bar), with the two red wires in it?
Presumably you have two red, two black, and two earth feeding that light?
That’s a yes to 2 light fixtures

1st one

2 black
2 red
2 earth

2nd one

1black
1ted
1 earth
 
That’s a yes to 2 light fixtures

1st one

2 black
2 red
2 earth

2nd one

1black
1ted
1 earth
What I would check first, with power off, is disconnect the red and black at the switch, and with no bulbs in the light fittings, use the multimeter on ohms range, check there is infinite resistance (ie open cicuit) between black and red. Not ideal, but at least would rule out a direct short in this section. Have you done any simple continuity checks to see if any miss connections?

I'm not clear if you have the new lights installed, or if wires are still hanging from the ceiling? Are new lights now in place, or are cables still disconnected?
 
Last edited:
Please could you explain the series of events that lead to the breaker tripping?
Did it trip when you first turned the power back on after wiring the lights,
or did you switch the power on, nothing happened, then you pulled the switch cord, and the breaker tripped?
If the second, the pull switch might now be welded permanently on!

Normally one would expect to test a circuit before applying power to it, though that doesn't seem to be the DIY way!
 
What I would check first, with power off, is disconnect the red and black at the switch, and with no bulbs in the light fittings, use the multimeter on ohms range, check there is infinite resistance (ie open cicuit) between black and red. Not ideal, but at least would rule out a direct short in this section. Have you done any simple continuity checks to see if any miss connections?

I'm not clear if you have the new lights installed, or if wires are still hanging from the ceiling? Are new lights now in place, or are cables still disconnected?
The lights were installed before (by me) and worked fine, it’s when the old switch was faulty and I’ve gone to install the new one I’ve had problems of it tripping out. I just took a photo of the old wiring and copied it to the new switch
 
The lights were installed before (by me) and worked fine, it’s when the old switch was faulty and I’ve gone to install the new one I’ve had problems of it tripping out. I just took a photo of the old wiring and copied it to the new switch
OK I understand better, thanks.
It seems obvious to concentrate on there being something wrong in or around the new switch.
The way you've described wiring it is how I would have done it!

Do the lights work all of the time, and the mcb trips only sometimes, or how does the tripping manifest itself?
 
OK I understand better, thanks.
It seems obvious to concentrate on there being something wrong in or around the new switch.
The way you've described wiring it is how I would have done it!

Do the lights work all of the time, and the mcb trips only sometimes, or how does the tripping manifest itself?
As it is now ( or was when wired as everyone including me assumed was the correct way) it would work for a bit then trip out, I’ve decorated since the dodgy switch started being dodgy and as a typical tradesmen the wife keeps reminding me every f’n year to sort it it and this year seems the year ! So basically recently the lights have been removed and wires hanging down ( it’s fine it’s adults only house!) and the string tied up . When some one not familiar with it would pull the cord it would trip and you have to pull again otherwise it would constantly trip.
 
Tbh it could possibly have been the wiring but I just assumed the switch was broken so replaced it but just coped with no bathroom light for about 4 years lol
 
As it is now ( or was when wired as everyone including me assumed was the correct way) it would work for a bit then trip out, I’ve decorated since the dodgy switch started being dodgy and as a typical tradesmen the wife keeps reminding me every f’n year to sort it it and this year seems the year ! So basically recently the lights have been removed and wires hanging down ( it’s fine it’s adults only house!) and the string tied up . When some one not familiar with it would pull the cord it would trip and you have to pull again otherwise it would constantly trip.
Well from everything you've said it seems there has been, and still is, a long standing fault, where if the switch was on, the MCB would trip. That implies somewhere between the light switch and the last light fitting, there is a problem with the wiring. The fact that an MCB trips and not the RCD (assuming the latter works - have you tried the test button recently?) implies to me a more serious problem.
I think either you should get a professional in with a multifunction tester to investigate, or as a minimum, replace the cables in the ceiling with new, all the way from the switch to the first light and then to the second light.
 
I’ve just got my multi meter in the wires in the loft the blue and brown is showing no reading and the read and black a tiny one I’ll include a pic and show the settings on my multi meter, obv the wires are all dangling so if I’m supposed to be connecting 2 lives I’m not. Cos ones not live and the other minimal
 

Attachments

  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    492.1 KB · Views: 13
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    image.jpg
    580.3 KB · Views: 16
photo of the wiring in the loft it leads to this switch
 

Attachments

  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    E3175DEF-C295-4151-9F72-0C29E21F5C0F.jpeg
    522.8 KB · Views: 18
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    D0F26887-AA63-43BC-B336-6EB05EA2D1FC.jpeg
    274.7 KB · Views: 17
  • [ElectriciansForums.net] Can anyone help with my bathroom light pull chord switch?
    5BB0E538-C757-44D5-A3E5-8B5344A0EC82.jpeg
    533 KB · Views: 17
So maybe this is where the issue is as there’s only one live wire here and I’m assuming there were 2 lives needed connecting, maybe the switch was being used as some kind of junction box and the switch was thswitch?

The switch isn’t in the bathroom and obv that wiring is new , I’ve discounted that switch as nothing as it “didn’t work”, it’s in a room connecected onto the bathroom by a door and this room was knocked into one massive bedroom before we moved in. I redid the partition and that switch never worked and so that’s where my problem maybe?
 
photo of the wiring in the loft it leads to this switch
I'm trying to make sense of those first two pics. This seems to be the problem.
the metal clad switch with the red, yellow, blue wires coming out of it seems to be a two way switch to operate the bathroom light in conjunction with the pull cord.
If the brown and blue wires leading off to the left go to your pull cord, then the old (broke) pull cord switch was being used two way. The bare copper earth wire is being used as the common live.
So it's not an earth wire at all!
If you want to continue to use that metal switch in pic 2, then that bit of brown/blue cable in pic 1 needs repacing with 3 core to the light switch. I think the problems you have been having are all because the earth wire is being used as a live wire, and now that is a problem at the new pull switch.
Is your new pull switch 2 way?
Can you replace the 2 core cable with 3 core without too much difficulty?

getting somewhere now !
 
I’ve just got my multi meter in the wires in the loft the blue and brown is showing no reading and the read and black a tiny one I’ll include a pic and show the settings on my multi meter, obv the wires are all dangling so if I’m supposed to be connecting 2 lives I’m not. Cos ones not live and the other minimal
In addition to the other recent discoveries, the leakage across red and black just using a multimeter is a bad sign.
You need an insulation resistance tester to check the resistance at 500V. Have you got a friendly sparky who could do that for you?
 

Reply to Can anyone help with my bathroom light pull chord switch? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

  • Question
"Value engineering."
2
Replies
39
Views
4K
I’m switching out timer light switches for normal light switches in my bathroom. One went to a light and fan and the second went to another light...
    • Like
Replies
0
Views
1K
I think I'm right in saying you cannot use the fused spur you have bought to replicate the circuit that's wired. You appear to have a fan with an...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks