Went to investigate zero output on solar system and discovered a damaged panel.
But what surprised me was the damage (Obvious heat damage) to the underlying sub-frame and roof membrane.
[ElectriciansForums.net] Panel and underlying damage.
[ElectriciansForums.net] Panel and underlying damage.
[ElectriciansForums.net] Panel and underlying damage.

The DC cabling was surprising un-marked.
Client is adamant that there had been no impact damage!
[ElectriciansForums.net] Panel and underlying damage.
 
Based on the crazing in the glass, it's probably some form of tempered/hardened glass... the stresses in it can cause it to spontaneously shatter (happened to my parents patio doors one afternoon and to a double glazed unit in the bathroom in the middle of the night).

After that it probably suffered an electrical failure that caused a small fire. Certainly makes you think when you see houses with them all over the roof, especially if like that they are the 'built in' variety.
 
Based on the crazing in the glass, it's probably some form of tempered/hardened glass... the stresses in it can cause it to spontaneously shatter (happened to my parents patio doors one afternoon and to a double glazed unit in the bathroom in the middle of the night).

After that it probably suffered an electrical failure that caused a small fire. Certainly makes you think when you see houses with them all over the roof, especially if like that they are the 'built in' variety.
Thanks, its certainly something to consider as a possible cause but nowt that we can do about that occurring.
Out of warranty now so no come back on supplier even if it could be proved that the panel was originally faulty.
My biggest surprise was the heat that had obviously been generated to cause the meltdown and how easily a fire could start through a faulty panel!
 

Reply to Panel and underlying damage. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

You need to pass the job on to someone who is competent and up to speed with solar installs and regulations .
Replies
4
Views
543
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
Thanks. This is what I have being trying to explain to the installer, but at the time I was just pleased that the system was up and running (solar...
Replies
6
Views
4K
Lol, wifi sticks are also low stock / no stock. My inverter has just been pushed back from early Sept to Mid Nov, its a jungle out there...... :)
Replies
11
Views
3K
  • Question
Hot water has to be stored at 60C+ and water temperature at the taps should be about 50C, If I have been told by people at work who flush and...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks