Honeywell V4073A1039 3-port microswitch not being activated?
OK so I looked at the microswitch last night and realised it was set into the middle position.
Have changed to be locked in to auto and heating came on first time last night without restarting the boiler.
However in the early hours of the morning from 0500 onwards and throughout the day the pump is still operating without heating or hot water being on.
The pump just came on now and checked the boiler and it wasn't firing up or anything and the boiler temp was 13c so frost protection wouldn't have kicked in.
Just need to stop the pump randomly coming on now so maybe I do need a new microfilter?
-
Nearly Esteemed
Arms
Supporter
Just need to stop the pump randomly coming on now so maybe I do need a new microfilter?
Assuming I've been looking at the correct boiler manual
and your Grundfoss pump external to the bolier is wired to the boiler connector (X16) for pump overrun, I see that port to which it's connected is multipurpose, is factory set for an external pump, but its use can be changed in setting D.026
I just wonder if that setting has got accidentally changed to other than 1? or 2. I don't know if anything different would happen with incorrect settings, but I guess it's worth checking what D.026 is set to?
If pump overrun were not required, for a Y-plan system I think the pump would normally be connected across the boiler - eg boiler switched live and neutral etc. So the pump could only come on when the boiler was on.
Reply to Boiler failing to respond to thermostat and has to be restarted in the Central Heating Systems area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
As a "temporary" measure I went down a slightly different route.
Nothing off the shelf appealed. In particular I wanted something with a good WAF...
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...