Honeywell V4073A1039 3-port microswitch not being activated?
OK so I looked at the microswitch last night and realised it was set into the middle position.

Have changed to be locked in to auto and heating came on first time last night without restarting the boiler.

However in the early hours of the morning from 0500 onwards and throughout the day the pump is still operating without heating or hot water being on.

The pump just came on now and checked the boiler and it wasn't firing up or anything and the boiler temp was 13c so frost protection wouldn't have kicked in.

Just need to stop the pump randomly coming on now so maybe I do need a new microfilter?
 
Just need to stop the pump randomly coming on now so maybe I do need a new microfilter?
Assuming I've been looking at the correct boiler manual 🤔 and your Grundfoss pump external to the bolier is wired to the boiler connector (X16) for pump overrun, I see that port to which it's connected is multipurpose, is factory set for an external pump, but its use can be changed in setting D.026
I just wonder if that setting has got accidentally changed to other than 1? or 2. I don't know if anything different would happen with incorrect settings, but I guess it's worth checking what D.026 is set to?

If pump overrun were not required, for a Y-plan system I think the pump would normally be connected across the boiler - eg boiler switched live and neutral etc. So the pump could only come on when the boiler was on.

[ElectriciansForums.net] Boiler failing to respond to thermostat and has to be restarted
 

Reply to Boiler failing to respond to thermostat and has to be restarted in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

As a "temporary" measure I went down a slightly different route. Nothing off the shelf appealed. In particular I wanted something with a good WAF...
Replies
7
Views
1K
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top