4mm for a 3.4kw oven? | on ElectriciansForums

Discuss 4mm for a 3.4kw oven? in the UK Electrical Forum area at ElectriciansForums.net

maccaandy

DIY
Joined
Jan 5, 2023
Messages
10
Reaction score
5
Location
UK
Hi,

I’m trying to replace a cable to an oven. The oven is 3.6kw total connected load. It requires approximately 25m run and the cables are clipped direct to a wall. I was going to use a 2.5mm cable but when I opened the isolator it has 4mm cable in there.

I think my calculations are correct in that I can run it with 2.5? Could someone just confirm that I’m not going mad?

Thanks,

Andy
 
Below is cable calc for 25m Clipped direct.
 

Attachments

  • [ElectriciansForums.net] 4mm for a 3.4kw oven?
    cable calc.PNG
    22.6 KB · Views: 46
Well, it’s a bit weird what’s been done. It’s currently on a 32amp with a 6mm radial. The 6mm radial then splits into two 4mm to supply two ovens.

I’m wondering if I just put two 4mm in then and put them on a single 32amp?
 
Ideally I like to keep the same sized cable throughout , but 4mm is so much nicer to terminate so in this situation I would probably drop down to 4mm off the 6mm if all backed up by a 32a
 
Ideally I like to keep the same sized cable throughout , but 4mm is so much nicer to terminate so in this situation I would probably drop down to 4mm off the 6mm if all backed up by a 32a
Ok thanks. So that’s what currently is there. 6mm cable to a junction box, and 2x 4mm going to the ovens - all backed up by 32amp breaker. That’s ok to do?
 
Ok thanks. So that’s what currently is there. 6mm cable to a junction box, and 2x 4mm going to the ovens - all backed up by 32amp breaker. That’s ok to do?
Assuming the JB is rated above 30 amps , is installed correctly and accessible for testing

6mm and 4mm cables is fine on a 32amp so long as its not running through loads of insulation etc
 

Reply to 4mm for a 3.4kw oven? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
To be honest James I use an app- Electrical Calculations. It auto calculates the cable size once you enter the specifics/parameters. Voltage...
Replies
5
Views
1K
  • Question
Personally I'd always fit 6mm. There was a thread on here a month or two ago where an electrician had run 4mm on a 32A breaker, another...
Replies
6
Views
3K
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
967
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks