Is new cu required for new oven install? | Page 2 | on ElectriciansForums
Discuss Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net
Jules123
High Wycombe
An electrician has recently quoted to replace our old oven. He says that the new oven has different power requirements and he needs to replace the consumer unit to make this lower and avoid burning out our new oven within weeks! The cu was new in 2015 so I am concerned that it now needs replacing - this will cost double the cost of the oven... Help please!
Echoing the sentiment of most posts above, i think we can agree in summary that it is the electrician that needs replacing, not the distribution board.
following the absurd explanation about a 40A supply burning out a 20A oven in weeks, its incredible that we have all survived the change to led "light bulbs" as they generally use about 90% of the power. so an original 6A lighting circuit should be burning out the new lights within minutes!! :) ;)
So the old cooker is connected to a 40A breaker and the new one only needs a 20A breaker.?? Is this correct?
I'd consider getting another electrician in to quote for the job...
Maybe there is an electrician on the forum that lives near you (High Wycombe) that could give you a quote.
Thanks for replies everyone. Looks like we need to keep looking for an electrician! Had two quote so far and need someone for some kitchen electrics as cowboy kitchen fitters had to be let-go. They were damaging the units! Dream kitchen not going so well atm 😟
He's either lying or totally incompetent!
If the new oven is only 20A than the MAXIMUM it can draw is 20A.
It doesn't matter that the supply is suitable for up to 40A, the oven can only draw up to 20A .
This is pretty basic stuff for an electrician!
So, regulations:
Since the oven is known as a fixed load in electrical terms, the existing 40A supply can remain as is without the need to change it - merely connect the new oven. (Although if I had a suitable smaller MCB closer to 20A I would probably change it - but it isn't mandatory)
However, it may be the case that your existing installation doesn't have RCDs (although given the age it should) in which case it should be upgraded - for more than the oven!)
Do you have a photo of the board?
[ElectriciansForums.net] Is new cu required for new oven install?
He said it only had one rcd??
Don't think your images worked. Copy and paste works well on this forum for images by the way.
Even if not RCD protected I'd still change a broken appliance.
New oven is 4.7Kw. A 'standard' 6 sq mm cable and B32 cooker circuit would be fine. Subject to seeing pictures, it sounds like you should find a different electrician.
There are 2 RCDs in that unit, they are the two devices labelled as RCCB.
Whilst I tried to give some benefit of the doubt earlier I would say this confirms you have been outright lied to.
I see no reason why that 40A MCB couldn't simply be swapped for a 20A MCB if that is required, those MCB's are current and still available.
There may be some mention of that CU being plastic when these days we are required to fit metal ones, but that would not prevent the work as you have described it from being carried out.
I am having the worse time with incompetent traders atm so glad you guys have all taken the time to tell me what's what. Thought it was bizarre that a replacement oven was such a problem!...
Nothing wrong with that consumer unit. (ish)
It has two RCDs!
He can't even count.
You could get the 40A MCB changed to a 20A or 25A, they are available if you want.
Now, it is the case that that consumer unit does not meet current standards, but in itself that doesn't mean it has to be changed.
If there is any sign of heat damage and/or a couple of other things, then it should be changed.
But from your photos, there is no evidence that a change is mandatory.
The rules have changed since your CU was installed. Yours is plastic, and only steel ones can be fitted in domestic properties now, but the rules aren't retrospective, so as long as individual parts are available for it (which they are) it doesn't need to be changed.
It has two RCDs!
Thanks so much for your time Julie! Super helpful 👍
Frankly I beleive that he has breached trading standards in that he has suggested you must have something that actually you do not need. This is fraudulent and he could be prosecuted for such fraud.
It would be an interesting case,
Although we can install things into what would be considered non compliant distribution boards by todays standards, and in many cases (including this one by the sounds of it) we should be doing so.
it could be argued that we are under no obligation to do any work that fails to comply with the letter of the latest standards.
the issue to me is how it is put to the customer. there is a difference between
I wont do that
and
i can't do that (with the inference that they would be breaking the law to do such)
Yes it would be. I think he mis-represented the truth with a view to gain a pecuniary advantage. If he would have said it is recommended or best practive etc, to supply SPD AFDD RCBO RCD ad nauseam that is different to presenting a scenario where he can't install the oven if you do not pay for the "necessary" work. It is fraud pure and simple.
whereabouts in High Wycombe are you
Hi Jules im in wooburn green.. if you want to get in contact
Click on their name in the conversation and then click start conversation.
  • [ElectriciansForums.net] Is new cu required for new oven install?
Thanks for all your feedback on this. Glad my gut made me check this. So fatigued following cowboy builders cobbling our kitchen together and damaging it in the process that not sure I have the energy (or time now we're doing the rest DIY) to chase him down but agree he is behaving in a fraudulent manner. Makes me wonder whether he's even fully certified. It was a local recommendation!!
A little update...went round to see the job on wednesday morn, Dual RCD board, 40 amp mcb for cooker circuit, 6mm cable and new oven is 5.1Kw, absolutely no reason for a new board or mcb, An extra double socket is required in kitchen so the only thing that needs doing is upgrade Type AC Rcd to a Type A......The so called sparks was trying to pull a fast one and had no clue what he was talking about
Nice one!
Reply to Is new cu required for new oven install? in the UK Electrical Forum area at ElectriciansForums.net
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
There are 3 spare ways available with a bit of re jigging. You wouldn't add a new circuit to any cu that wasn't fire retardant?
4K
Needs to be established whether the supply to the cooker isolator + socket is suitable to supply both oven and hob, after diversity is taken into...
4K
M
I meant EIC, No idea why I put EICR down, thanks for the clarification
Hello, No nothing. No electric car or solar. Nothing out the ordinary. Also to be clear. I have two RCD? Boards. One old house one new, the...