Discuss Why does my main house consumer unit trip when the inverter switched to AC backup? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Is the cabinet earthed back to the main db earth bar? Ie is the earth bar connected the the earth of the ac input c form socket?Hello again Marconi
I followed the instructions and got the AC to charge the batteries with the USB timer set and it was charging for a short while.
I followed the instructions one at a time and then turned on the Solar Consumer unit. I then ran a kettle on the kitchen circuit and the microwave on a separate circuit serving the extension this took the output to 3Kw so I added an induction hob which took the output to 5.1 Kw, the max of this inverter being 5.5Kw I believe.
At this point the MEM rcd has not tripped and until I get another couple of sockets added to the next MCB circuit I can only add to the two I have at present with more items. I am surprised the mem did not trip but this may be as a result of only 2 mcb currently pulling power through the consumer unit.
Let me know your thoughts regarding this test and I look forward to trying some more experiments before I remove the unit to return to the supplier.
I have been testing all of my pv wiring in a last ditch attempt to see what is causing my dc.dc overcurrent issue but with no obvious problems with the wiring I am resigned to returning it to the supplier next week.
regards and thanks as ever for the help
Tonyboy
Dear
Good morning. I wondered if have had time to consider what I sent you? With further research and testing of the Axpert MKS iv 5kW solar inverter fitted in my clients SP5048 off-grid plug and play panel I pretty convinced in my own mind that the tripping of the up-front RCD is because there is an N-E link made inside the Axpert box. Interestingly, I have discovered that for the equivalent (same?) Voltacon or Conversol branded solar inverter there is no internal N-E link. Instead one can buy this unit which makes the N-E link externally whenever the inverter is supplying the output, otherwise ie in bypass mode it is disconnected because the N-E link is made upstream from the supply. Perhaps you could review the links above for me please?
Regards
Good morning Marconi.Is the cabinet earthed back to the main db earth bar? Ie is the earth bar connected the the earth of the ac input c form socket?
Good morning MarconiI think those voltage measurements are unsurprising but to be sure would you draw me a diagram which shows accurately what each earth terminal is connected to and between?
Also show how you made your voltage measurements and the readings. I normally do this by a V in a circle with two leads from it to the two points across which I measure a voltage.
The F12 fault could indeed be due to an pv over voltage measurement. But, I think you said the system functions normally even with F12? This over voltage could be a result of the way the earths are connected and to what hence my first paragraph.
Hello MarconiPlease send me a link to what you have read on earthing on the V Ltd website. The earthing and bonding of your installation is something we need to get right mindful that your supply is PME which has restrictions on using the Main Earth Terminal (MET) outside the 'equipotential zone' generally and simply understood in the domestic setting as anything within the home.
Please send me a link to what you have read on earthing on the V Ltd website. The earthing and bonding of your installation is something we need to get right mindful that your supply is PME which has restrictions on using the Main Earth Terminal (MET) outside the 'equipotential zone' generally and simply understood in the domestic setting as anything within the home.
Hi MarconiPlease send me a link to what you have read on earthing on the V Ltd website. The earthing and bonding of your installation is something we need to get right mindful that your supply is PME which has restrictions on using the Main Earth Terminal (MET) outside the 'equipotential zone' generally and simply understood in the domestic setting as anything within the home.
Hello MarconiHave you reported the state of the inverter on/off correctly for voltages 1 and 2 above? I would expect voltage 2 when the inverter is off to be round about 7 x 50 = 350V and voltage 1 when the inverter is on and MPPT operating to be lower eg your reading of 246V. The open circuit voltage of a panel is about 50V.
The 130-170V reading of the array metalwork to earth rod is to be expected due to the distributed insulation resistance of the panels and cabling to ground. For evenly distributed insulation resistance to earth the voltages would be half the +ve to -ve voltages so 350/2 = 175V and 246/2 = 123V - near enough what you measured.