[ElectriciansForums.net] Does this henley block on the incoming tails of TT have a fuse in?
 
Well that’s not confusing in any way…. Brown used for line and neutral and then disappears behind the board.

Just asking for a polarity mix up.
Those browns are an old outer sheath colour,more a dark maroon really. the basic insulation will be red and black inside.
 
0.44 Meg ohm is 440000 ohms.
You are of course correct. I Think i'm confusing myself. I cannot see any bonding conductors in the CU, yet when I get my wander lead out and test from the only earth conductor in there to the stopcock pipework and gas meter I get 0.00 Ω on each despite not being able to see any bonding conductors or earth clamps anywhere. Also when testing the ZE I was looking at my Megger testing a disconected main earth cable to earth electrode and got a reading of 0.44mΩ. I had in my head Ohms. This is of course megaohms... I haven't seen a TT system for a few years and I think I need to read up a bit. Thanks for your help..
 
. I cannot see any bonding conductors in the CU, yet when I get my wander lead out and test from the only earth conductor in there to the stopcock pipework and gas meter I get 0.00 Ω on each despite not being able to see any bonding conductors or earth clamps anywhere.
This will be via the cpcs of cables to the boiler, immersion heater, etc.
 

Reply to Does this henley block on the incoming tails of TT have a fuse in? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Obviously you need to check the means of earthing, Ze, and polarity no matter what for the EIC. As above, if anything looks dodgy then EICR is a...
Replies
3
Views
547
  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
558
More important than torque, is to settle the strands of the cable as you tighten the screws. Pity that a few more meter installers aren't familiar...
Replies
4
Views
523
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
626
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks