Testing sqD GFCI breaker | on ElectriciansForums

Discuss Testing sqD GFCI breaker in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 5, 2023
Messages
3
Reaction score
0
Location
Michigan
Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or load 2 to N or load 1 to 2 they all start out @ 27ohms and increases to 45+ ohms, if I reset breaker ( it's out of the box) and test resistance from line 1 to load side 2 yes opposite side with breaker on I also have a rising ohm reading 27 and increasing to 39+ohms , I'm coming up with a faulty GFCI breaker that's leaking internally...... Am I on the right path ??? Or do I need to look at spa unit as having a GFCI fault some where
 
If it will energise and stay on when the supply is connected but none of the outgoing cables are connected then the unit is likely ok.
 
Ok. I will try that. I had pulled it to get a better bench test on it when I had seen the raising resistance, and didn't know if it had gotten moisture in it and caused a leak across the the poles or was creating a soft ground point, I never tested a GFCI breaker that had resistance across the load connection's, I was also told sqd breakers are not good for spa units. But at time of install that was all that was available 🤔 so I will try it out in morning..
 
What you see by way of rising resistance on your meter can be caused by eg a capacitor in an electronic circuit charging up (from the battery in your tester), not a fault! The gubbins below require power, so you will see resistance across some terminals from the power supply components.


[ElectriciansForums.net] Testing sqD GFCI breaker
 
Ok I see that it could be energizing the trip coil but wouldn't the 2 poles be separated and have there own sensing coil? And then be connected to the neutral line? I could see there being resistance from load 1 to neutral or load 2 but not load 1 to 2.. just a head scratcher gonna be testing in a few when I get home
 
Weekend sparker here, I have a sqd 2 pole 50amp GFCI breaker it was mounted out side in a service box, have not had a problem till now 3yrs old, it trips instantly when rest, with the breaker out of the box, I check resistance across the load side of the breaker from either load 1 to neutral or load 2 to N or load 1 to 2 they all start out @ 27ohms and increases to 45+ ohms, if I reset breaker ( it's out of the box) and test resistance from line 1 to load side 2 yes opposite side with breaker on I also have a rising ohm reading 27 and increasing to 39+ohms , I'm coming up with a faulty GFCI breaker that's leaking internally...... Am I on the right path ??? Or do I need to look at spa unit as having a GFCI fault some where
My suggestion is to replace the 50 amp GFCI breaker. Over time they will go bad.
 

Reply to Testing sqD GFCI breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
Replies
1
Views
708
I am living in the north of Thailand where the grid is very unreliable (rainy season outages multiple times per week or once a full week). I...
Replies
0
Views
416

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top