Currently reading:
Darkwood
Staff member
Mod
Supporter
There will be 1000s of brand new build houses and flats exactly like this with 10-15 metres of Tails snaking around the fabric of the build in the walls and under the floors. I see it all the time/
No Rcd , No isolator and no way of realistically checking checking if the entire length sits at 50mm+
Code 2 :)
A relative was looking at a new build house and we had a look while they were under construction. Had she gone ahead with the purchase, one of the things I planned to do was ask whichever scam the electricians were in why their members issued falsified certificates of compliance - I spotted 2 without looking, one of which would have been the unprotected tails between where they came through the walls from the fugly box up to where the CU was.
IMO Metre Tails should be visible for inspection from the meter to consumer unit , I really don't like them snaking 10-15mtrs through the fabric of the building up in the walls and in the floor voids. Just seems such a naff design.
Done some investigating this morning to ascertain why the earth reading is so high on the TT system I went to on Friday.
I’m hazarding a guess that this might be why.
That’s the water pipe to the property and they have done that because they couldn’t (or couldn’t be arsed to try to) get a rod in. Will find out shortly if I can or not.
It must go plastic shortly towards the supply side (or at least non-condictive joint(s) somewhere otherwise it ought to be better. Re-label as pipe bond?
Still, see what a proper rod does, but I guess recent rain so not quite a fair comparison? Other than actually being done right, of course....
So on further investigation. There is approx 2m of copper pipe, then there is alkathene back to the main pipe where the water meter is (house was only finished in Nov last year).
Anyway, after banging in 2 x 2.4m rods I’ve got the reading down to this.
And the Zappi works again.
What's in what I assume to be a fused connection unit ? Is that swa in / out or tails ?