I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

[ElectriciansForums.net] 3 x 2.5mm T&Es into one 13A socket. How do you do it?


Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

[ElectriciansForums.net] 3 x 2.5mm T&Es into one 13A socket. How do you do it?


Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
 
Seems like a lot of work for a problem that doesn't / shouldn't exist.

The only time I've had that issue is when refitting very cheap sockets where there isn't really enough space for the 3 wires or they have been cut too short and my fat paws won't fit.
 
It does mean less risk of things being disturbed when the socket is wraggled on to the back box. And the stranded singles will make things easier. As above though, quite a bit off faffing.

Be interesting to see what people think.
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Why not just use the

MK LOGIC RAPID FIX

 
Aren't you technically taking two spurs from one point of the ring though?

IE you have ring in and out, plus the third to your spur - but then the socket its behind is also a spur - as the point of junction is now the wagos rather than the socket faceplate
I agree, he's turned the existing socket into a spur.
 
Effectively picture #2 is what they do in America / Canada called PIG TAILING , they do it a lot over there using Wire Nuts to bind all the cores together in the back of the box and just take a single cable to the socket or as they call it the receptacle.
Most sockets will take 3 x 2.5 cores , except for the really cheap carp ones
 
never had an issue before... not with new, clean solid core. As you tighten the terminal screw, the cores will turn so the screw is gripping two cores, and the other is pressed into the back of the hole.
Never twist together.

stand by for other manufacturers following MK..... Still not used one yet, but i can see it being a time saver if fitting out an entire house.
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Will you be going back to the jobs to correct them ?
 
I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket.

The three solid cores rarely sit cleanly, and there's always the suspicion that at least one core is not being held properly:

View attachment 109255

Lately I've been doing this, using 5-way Wagos and bits of stranded 2.5mm single, fitted with ferrules, into the socket itself:

View attachment 109256

Of course that's more joints. Perhaps unnecessary joints. But it appears to me a more secure and more maintenance-free method.

I don't believe there's any regulatory reason why it can't be done like this.

What do others do/think?
Ridiculous in my honest opinion
 
Will you be going back to the jobs to correct them ?
Why would he go back and correct them, yes its a technical breach of the regs but there's nothing dangerous in what he's done, its still the same number of sockets in the circuit its just that the joint is in the wago and not the socket, those wagos can withstand about 100 amps before they melt according to several video's I've watched on them. I would only ever go back to a job if I realised I'd done something dangerous.

Saying that, its well over the top, those wagos are about 20p each, a pack of ferules, cable ties, 3 coils of conduit cable, might as well not bother doing the job at all. I don't get why people end up with spurs on new wiring anyway, I work with someone who always manages to do this, there is always a socket somewhere that has 3 cables at it on one of his re-wires, it cant be that hard to go in a circle can it
 
Pig tailing / splicing / the cables in the back of the box like this using Wagos really isn't an issue as long at the linking single cable is 2.5 or bigger and the OCPD is 32amps or lower.
Wagos are pretty much bomb proof and would run 30amps all day long without so much as breaking a sweat
 
Why would he go back and correct them, yes its a technical breach of the regs but there's nothing dangerous in what he's done, its still the same number of sockets in the circuit its just that the joint is in the wago and not the socket, those wagos can withstand about 100 amps before they melt according to several video's I've watched on them. I would only ever go back to a job if I realised I'd done something dangerous.

Saying that, its well over the top, those wagos are about 20p each, a pack of ferules, cable ties, 3 coils of conduit cable, might as well not bother doing the job at all. I don't get why people end up with spurs on new wiring anyway, I work with someone who always manages to do this, there is always a socket somewhere that has 3 cables at it on one of his re-wires, it cant be that hard to go in a circle can it
It was a question to the OP asking if he was going back to correct the non-compliant installation.

If you're happy to install from new, something that is non-compliant that's on you, personally I wouldn't do it because I wouldn't want anyone in the future to drop the socket and think WTF.

Doing what he did has made it less safe than joining them in the socket, he has introduced more joints and turned the original socket into a spur.
 
Last edited:
It was a question to the OP asking if he was going back to correct the non-compliant installation.

If you're happy to install from new, something that is non-compliant that's on you, personally i wouldn't do it because I wouldn't want anyone in the future to drop the socket and think WTF.
Is it actually non-compliant though?
 
It was a question to the OP asking if he was going back to correct the non-compliant installation.

If you're happy to install from new, something that is non-compliant that's on you, personally I wouldn't do it because I wouldn't want anyone in the future to drop the socket and think WTF.

Doing what he did has made it less safe than joining them in the socket, he has introduced more joints and turned the original socket into a spur.
I wouldn't do that either but if I did do something that later turned out to be a technical breach but was perfectly safe I wouldn't be going back to alter it. Especially after seeing the cowboy stuff from otheres that is churned out on a daily basis without a care in the world.
 

Reply to 3 x 2.5mm T&Es into one 13A socket. How do you do it? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
  • Question
Watching too many Aussie Gold Hunter video on YouTube. Be nice if they were though, make the weighsies more worthwhile.
Replies
6
Views
2K
Cut/slit the wallpaper with a knife Drill a hole from above the skirting to under the floor Get yourself a fish wire(make a eye to fix the cable)...
Replies
4
Views
5K
To me they look like 2 conductors covered in black heat shrink/sleeving/neoprene, they don't look brown at all but there again I have old eyes
Replies
34
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks