A client wants an outdoor socket installing on a new circuit. The current installation doesn't have any RCDs for the other circuits. I would put the new circuit on an RCBO but I'm concerned about signing off the installation with the other circuits not protected by RCD. Anyone know what the rules are here? When completing the EIC, my understanding is that you are effectively signing off the entire installation. I stand to be corrected, but please let me know where this is written down. Thanks


[ElectriciansForums.net] New Circuit - NO RCDs
 
Age of install, 2005ish with duel colours…. Shouldn’t at least downstairs sockets would have rcd from new?
Edit.
The few blanks in the middle might suggest an rcd was once fitted in the middle, but it’s been removed for whatever reason.

have you had the cover off? Just one busbar?

If it has been converted from split board, you could “repair” and at least get all the sockets on rcd.

Or try to upscale to a replacement full RCBO board
 
Last edited:
Your Certificate covers your work only, obviously check main protective bonding. State on the Certificate the exact extent of works.
Thanks westward10.

So, on the schedule of inspections, I just answer the questions in relation to the new circuit not the old ones? And on the schedule of test results, just fill out the test results from the new circuit? I could also write about the other circuits not being protected by RCD in the comments box?

It's my first time doing a new circuit on an old CU with no RCDs.
 

Reply to New Circuit - NO RCDs in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

IMO the NICEIC and NAPIT are two quangos that have made a laughing stock of the UK's electrical industry aided and abetted by the Labour...
Replies
10
Views
1K
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
1K
  • Question
Nope, totally fubar.
Replies
15
Views
2K
  • Question
You'd have to be mindful of SPD conductor lengths doing it that way. I think Matt:E make a single board with Type A RCBO, openPEN detection and...
Replies
1
Views
844
Thought I'd update this. Finally had my assessment today. I chased them on Friday morning as it'd been about 10-12 weeks since I'd actually made a...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks