I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR.
I know you have to do one 1st fix at 500V DC and then final one at 250V DC when all cables.
What I'm confused about is GN3 states:
"...sometimes these cables are terminated without further testing. This is no longer acceptable: it is now essential to test the protective conductor (such as armouring) with this connected via a fly-lead if necessary. To the installation earthing arrangement."
In other words it means IR testing the lines conductors clamping to the Banjo. The banjo will need a temporary connection to the MET for test purposes. (fig 2.23 shows an example of that)
Does that mean steel containment conduit will require this as well as its not specifically mentioned neither its used as a protective conductor.
Thanks people!