Hi,
I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR.
I know you have to do one 1st fix at 500V DC and then final one at 250V DC when all cables.
What I'm confused about is GN3 states:

"...sometimes these cables are terminated without further testing. This is no longer acceptable: it is now essential to test the protective conductor (such as armouring) with this connected via a fly-lead if necessary. To the installation earthing arrangement."

In other words it means IR testing the lines conductors clamping to the Banjo. The banjo will need a temporary connection to the MET for test purposes. (fig 2.23 shows an example of that)

Does that mean steel containment conduit will require this as well as its not specifically mentioned neither its used as a protective conductor.

Thanks people!
 
Does that mean steel containment conduit will require this as well as its not specifically mentioned neither its used as a protective conductor.
IMHO the principles are

1 - Sensible testing during installation e.g. making sure singles in steel conduit are not damaged and in contact with the containment, or the conductors in MICC are not breaching the outer copper core

2 - Mandatory 500v tests prior to loads / accessories being fitted with everything that is going to be earthed and bonded connected to the earthing system. This includes the armour of SWA, or steel trunking or conduit. Usually glanding into the switch gear and fitting banjo's / earthing nuts will achieve this.

3 - Mandatory final 250v tests when 2nd fixed.

For the mandatory IR tests to be valuable the earthing system needs to be completely intact. It can sometimes create challenges but we always find a way don't we!
 
Ahh, I see so in other words your saying on your no.2 point.
Connect the CPC earth and fly lead bonding of the steel conduit to the earthing arrangement. (using wander lead maybe)
Then test at 500vDC

Thanks it has cleared it the way you said it.
 
The reason for testing with all the CPC & metalwork to the MET is to catch a situation like T&E with one of the live conductors nicked by a screw. If you test L-CPC alone (with CPC floating) that might be perfectly good if the screw has not breached both and you would not see the fault.

However, with the CPC to the MET and thus to the Earth at large (and hence now to the screw) there is a good chance you will see the fault as a suspiciously low IR for brand new cable, more so if you see something like >299M for N-CPC and, say, 10M L-CPC, then something is clearly not right even though at this point it actually passes the usual thresholds, etc.
 
Ahh, I see so in other words your saying on your no.2 point.
Connect the CPC earth and fly lead bonding of the steel conduit to the earthing arrangement. (using wander lead maybe)
Then test at 500vDC

Thanks it has cleared it the way you said it.

I can't see a need for any wander lead or temporary connection for IR testing, what do you think needs a temporary connection?

All of your conductors should already be connected by the time you do the testing.
 
I can't see a need for any wander lead or temporary connection for IR testing, what do you think needs a temporary connection?

All of your conductors should already be connected by the time you do the testing.
Hi, Sorry for late reply.

To my understanding of the GN3 Amendment 2 it states it here during install and then after install.
1st test: 500V IR test with the protective conductor connected to the earthing arrangement.
2nd Test: 250V with everything in place (except sensitive equipment obviously)
 

Attachments

  • [ElectriciansForums.net] Insulation Resistance Testing Am2 - requires to be tested twice
    20230820_125635.jpg
    441.2 KB · Views: 19
I think that's the rough idea, though the sensitive equipment IS connected for the second test, and no insulation test is carried out L-N for that test. That's how we do it anyway. If the equipment can't take 250V between live conductors and earth, it shouldn't be connected to the supply at all.

I like how that tester switch is labelled 'insolation'...

Edit, I've just see this is another old thread...
 

Reply to Insulation Resistance Testing Am2 - requires to be tested twice in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top