Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used inaccurately.
I had an EV charger installed in December on my detached garage by a local electrician. The charger is one that doesn't have a PEN fault detection device (Tesla), hence we agreed I'd get it separately (Search Results - Detail - https://www.garo.co.uk/product-details/All/G6EV40PME).
Armoured 10mm^2 cable (from main circuit board to garage - approximately 32 meters) has been used to the garage where a smaller consumer board and the PME fault device was fitted. From there there's around 4-5m of 4mm cable to the actual charger.
After awhile I've noticed that the PME fault device trips every now and again - always late in the evening or at night, although that's mostly when I charge. It is quite sporadic, although in reality probably happens every 5-6 charges, which can be annoying in the morning if I miss the message on the car's phone app.
Interestingly the Tesla charger integrates with my Home assistant, so I can see the voltage at the charger, which seems to significantly drop on some evenings/nights (expected under load?), although never below the PME device's 207-253V range.
I have raised this with the electrician several times and he's not sure why this is happening. Also everything seemed fine on the 2 occasions he's tested it - once after installing and later when I raised the problem with him. However the test was never done by him at the time when voltage significantly dropped.
I did measure the voltage myself once when the voltage seemed low, soon after the PME device tripped and I reset it. In the house - ~232V, in the garage's consumer unit - ~230V, meanwhile Tesla charger in Home Assistant reported approx 222V while charging.
Question - where would I go from here ? Is there anything obvious another electrician would perhaps notice.. ?
Some photos attached.
Thank you
I had an EV charger installed in December on my detached garage by a local electrician. The charger is one that doesn't have a PEN fault detection device (Tesla), hence we agreed I'd get it separately (Search Results - Detail - https://www.garo.co.uk/product-details/All/G6EV40PME).
Armoured 10mm^2 cable (from main circuit board to garage - approximately 32 meters) has been used to the garage where a smaller consumer board and the PME fault device was fitted. From there there's around 4-5m of 4mm cable to the actual charger.
After awhile I've noticed that the PME fault device trips every now and again - always late in the evening or at night, although that's mostly when I charge. It is quite sporadic, although in reality probably happens every 5-6 charges, which can be annoying in the morning if I miss the message on the car's phone app.
Interestingly the Tesla charger integrates with my Home assistant, so I can see the voltage at the charger, which seems to significantly drop on some evenings/nights (expected under load?), although never below the PME device's 207-253V range.
I have raised this with the electrician several times and he's not sure why this is happening. Also everything seemed fine on the 2 occasions he's tested it - once after installing and later when I raised the problem with him. However the test was never done by him at the time when voltage significantly dropped.
I did measure the voltage myself once when the voltage seemed low, soon after the PME device tripped and I reset it. In the house - ~232V, in the garage's consumer unit - ~230V, meanwhile Tesla charger in Home Assistant reported approx 222V while charging.
Question - where would I go from here ? Is there anything obvious another electrician would perhaps notice.. ?
Some photos attached.
Thank you