This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help.

I installed an EV Charger a few weeks back, and all went well for a while, then the client called me to say it wasn't charging randomly. Resetting it brought it back to life. When we interrogated the logs we were seeing a combination of Earth Fault and PEN Fault errors.

I retested everything right through and found no issues with regarding earthing, continuity and IR. I even did a full EICR on the house, with no issues found. (It needed it anyway, as the client had requested a new consumer unit).

Both the manufacturer and the DNO have been contacted and they acknowledge the fault but they are also at a loss as to what it is.

The only thing I noticed is the incoming voltage. Normally I see a reasonably stable voltage at a property, but in this case it was wobbling all over the place from 230V up to 247V. Unfortunately the DNO will not send out an engineer unless the voltage falls outside the range of 213V to 253V. But I was thinking, if the voltage is unstable and it suddenly dropped below 213V could it cause the EV Charger to throw a wobbly and misreport an Earth Fault ?

The only other thing, is to check for current leakage on the earth, but I can't remember how I can monitor that.

Oh finally the RCBO's are not tripping when this happens.

Any thoughts welcome.
 
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help.

I installed an EV Charger a few weeks back, and all went well for a while, then the client called me to say it wasn't charging randomly. Resetting it brought it back to life. When we interrogated the logs we were seeing a combination of Earth Fault and PEN Fault errors.

I retested everything right through and found no issues with regarding earthing, continuity and IR. I even did a full EICR on the house, with no issues found. (It needed it anyway, as the client had requested a new consumer unit).

Both the manufacturer and the DNO have been contacted and they acknowledge the fault but they are also at a loss as to what it is.

The only thing I noticed is the incoming voltage. Normally I see a reasonably stable voltage at a property, but in this case it was wobbling all over the place from 230V up to 247V. Unfortunately the DNO will not send out an engineer unless the voltage falls outside the range of 213V to 253V. But I was thinking, if the voltage is unstable and it suddenly dropped below 213V could it cause the EV Charger to throw a wobbly and misreport an Earth Fault ?

The only other thing, is to check for current leakage on the earth, but I can't remember how I can monitor that.

Oh finally the RCBO's are not tripping when this happens.

Any thoughts welcome.
Hi, John Ward did a video on the effects of a broken PEN. What you have described sounds similar to the things shown on Johns' video.
 
If you think about it, in the absence of a well installed earth rod for a reference, lost PEN detection can only be by inference if the supply voltage goes out of range. So supply voltage out of spec == infer lost PEN.
 
If you think about it, in the absence of a well installed earth rod for a reference, lost PEN detection can only be by inference if the supply voltage goes out of range. So supply voltage out of spec == infer lost PEN.
Agreed, loss of N further down the network can give wildly changeable voltages
If it is tied to earth, then that will go up and down too.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
EV Charger reporting PEN Fault
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
3
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
vwes59,
Last reply from
James,
Replies
3
Views
858

Advert