A BG fused connection unit, with neon.
A boiler.
Fuse out. Spur switched off.

I was checking polarity after a colleague had 2nd fixed it and without thinking chose the load N not the supply N.
This led to discovering:
120v between Supply Live and Load N
120v between Supply Live and Load Live

I tried his 2 pole tester, same except that one said 50v.

Look at boiler end, all fine.
The strangeness stops when I disconnect earth at the boiler.

IR tests L-E and N-E at boiler (at 50v) were >99M

Should I conclude that there's are very very high resistance L to E and N to E paths inside the boiler and yet the impedance is low enough to light up a tester, or am I missing something embarrassingly basic?!
Thanks
 
[ElectriciansForums.net] Little mystery that's bugging me
[ElectriciansForums.net] Little mystery that's bugging me
 
Another possible explanation is that if the boiler has any sort of traditional interference filter in the mains input, this will lead to the 120V effect, as there is a capacitative divider across the mains, with the centre point earthed. This has cropped up on previous posts here with other appliances. It depends a bit on the impedance of the measuring device as to what voltage you see, but with high impedance you will get half mains voltage across each CY capacitor.
[ElectriciansForums.net] Little mystery that's bugging me
 

Reply to Little mystery that's bugging me in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
944
  • Question
Yeah I doubt it's normally an issue. Split load boards and SWA incomers are likely the only trouble.
Replies
16
Views
3K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
As above. Also PME doesn't exist outside the UK. Almost all installations within the State are TN-C-S - TT has pretty much been eradicated...
Replies
2
Views
3K
  • Question
There was also a run of the same brand's two pole SFU which had a pole not working...very anti-euro...
    • Like
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks