Hi everyone

Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too high so he was considering changing the circuit breaker back to B type as it allows enough Zs to meet the regulations.

As Afdds is also combination of Rcds so Zs would be 1667 ohms which someone mentioned to which he replied for earth fault loop yes but for L-N loop doesnt meet regulations hence the replacement.

Furthermore he says for L-N doesnt meet reg for short circuit thats why we do PSCC. If TNC-S arrangement then because of Neutral and earth are connected so we do not need to do PSCC and Prospect earth fault current would be same as short circuit.

As I am also in a learning stage so always mess up some concepts when I come across these questions so some questions emerged in my mind which if someone could answer and correct me if I am wrong .

My understanding was we carry out Ipf at origin to check if there is enough fault current generated if Supply side L-E comes in contact to disconnect Main cutout fuse or Circuit breakers hence we also consider short circuit capacity of MCBS.

By checking PSCC at origin we ensure that if L-N at supply side comes in contact it would disconnect main cutout fuse or MCBS.

on the load side afcourse as fault current depends upon the MCBs such as 32type B MCB would have minimum of 160A of fault current hence 230/160*0.95 would make 1.37 ohms resistance max to meet disconnection times.

Since the person mentioned he checked PSCC and it did not meet Zs so he is considering it back to type B, does he mean that, he carried out PSCC at supply side or towards load side on final circuits?
As on load side we usually carry out Zs to ensure it meets reg and since the Afdds contains RCD so it would meet regs.
Do you guys carry out PSCC on final circuits to see it circuit breakers would trip if short circuit were to happen like he did ? as my understanding was to only check Zs to meet regs and he said Zs was ok but PSCC was not met.
Straight after the post he took it off and I could not question him but the question is bugging me .
 
but would this then be treated like a TT with all conductors (but not busbars) needing to be double insulated until the first protective device, assuming the consumer unit was metal and an RCD was required for fault protection for outgoing circuits?
Having a L-E fault on the incomer is always a bad day, TT or TN!

These days you would be using double-sheathed tails anyway, and (hopefully) a proper gland for them, so you would meet that sort of "no single point of failure" anyway even with a metal CU.

Where it gets more complicated is a SWA sub-main, it is not double insulated in any real sense, though it has the metal armour for protection to a degree. I would be considering adequate protection to be placed before any such run (even if < 3m) so if you can't disconnect on any supply fuse safely I would be considering an up-front delay RCD.
 
Last edited:
Having a L-E fault on the incomer is always a bad day, TT or TN!

These days you would be using double-sheathed tails anyway, and (hopefully) a proper gland for them, so you would meet that sort of "no single point of failure" anyway even with a metal CU.

Where it gets more complicated is a SWA sub-main, it is not double insulated in any real sense, though it has the metal armour for protection to a degree. I would be considering adequate protection to be placed before any such run (even if < 3m) so if you can't disconnect on any supply fuse safely I would be considering an up-front delay RCD.
Yeah I doubt it's normally an issue. Split load boards and SWA incomers are likely the only trouble.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

King84

Trainee
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Question about Zs and PSCC needs some clarification thanks
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
King84,
Last reply from
Aaron b,
Replies
16
Views
3,745

Advert

Back
Top