As above plus
grey should be used a N with blue sheath.
armour is not earthed.
 
Perfectly acceptable to use black as the neutral conductor providing it is correctly identified.

The supply is using black as neutral and grey as earth. I would seriously question the competence of someone who cannot even get that correct.
 
Things wrong in this picture;

1. Basic insulation showing (meter cabs are not considered suitable enclosures) interestingly site applied insulation (heat shrink) is no longer classed as suitable in an application like this either.

2. Black being used as the N (personally don’t see a problem with it and I’m not aware of any regs which explicitly state black cannot be used as a neutral) but the NICEIC ran a campaign to “de-neutralise” the black. Bigger problem IMO is no sleeving to identify it as a neutral.

3. Difficult to tell from just a photo but that doesn’t appear to be a 25mm SWA and the cut-out says 100A fuse fitted. So OCPD is too large for cable.

4. Whilst not a 7671 reg most DNOs/DSOs specify that meter tails can only use the cutout fuse as an OCPD where the tails are less than 3 metres.

5. SWA braid is not earthed.

6. SWA is not terminated correctly.
 
Or not as the case might be.

Think there was a debate previously on the forum as to whether a meter box is considered an enclosure because it is lockable (don't laugh) and a key is needed!
According to NICEIC and Select it isn’t classed as a suitable enclosure as non-skilled persons access the enclosure regularly/to read the meter etc.
 
Glanding the cable to a metal fused-switch like the Wylex ones would have been far better, then double insulated tails to the meter.

It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?
[ElectriciansForums.net] Can anyone tell me what is wrong/incorrect.
 

Reply to Can anyone tell me what is wrong/incorrect. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
i think dan was referring to the OP where they mentioned it was found when removing mirrored wardrobes.... maybe nothing to do with the mirror...
Replies
9
Views
752
  • Question
Probably for an old TV amp as little spark said
Replies
4
Views
419
  • Question
Sorry for the late reply I found it very difficult to find work but I’m not sure if this was down to Covid and all the lock downs happening just...
Replies
2
Views
489
R
  • Article
Can anyone help me identify these bathroom taps please? Hi Can anyone identify the make and model of these taps please? We have one dripping...
Replies
0
Views
175
Richt5a
R
  • Question
Thanks James, that's very helpful, give s me loads to get sorted now, fingers crossed for a safe outcome.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks