Is this ok?

32amp breaker with a 6mm wire leading to fused cooker switch.

This then leads with 6mm cable to hardwire point.

Can i hardwire 2 x 16 amp appliances to this hardwire point.

This hardwire point is all i have for these these appliances. Should I use a double hardwire point or will a single be fine for both?
 
Last edited by a moderator:

Attachments

  • [ElectriciansForums.net] Can i hardwire two 16amp aplliances into a hardwire point on a 6mm cable?
    Oven Install.png
    27 KB · Views: 40
Each appliance will require a 16a fuse or mcb. With your stated arrangement this will not be easy to achieve. The options are you split the existing 6.0mm/32a supply through an enclosure with 2x 16a mcb's, and from there to two outlets.Or drop the existing 32a supply to a 16a mcb and use that for one, and run another 16a radial back to the db for the second.
 
Thanks for the help. Gonna run a new wire 🤪

So just a quick one. Why do you need a 16amp breaker on a 6mm wire? If the appliance is rated at 16amp then is the reason for keeping the breaker at 16amp and not maxing at 32amp incase the appliance is faulty and drawns too much power?
 
Thanks for the help. Gonna run a new wire 🤪

So just a quick one. Why do you need a 16amp breaker on a 6mm wire? If the appliance is rated at 16amp then is the reason for keeping the breaker at 16amp and not maxing at 32amp incase the appliance is faulty and drawns too much power?
Yes, it's about what happens when there's a fault.
If the manufacturer of an appliance specifies overload protection for it (eg a 16A), then an electrician installing it is obliged to take heed of that recommendation.
The need for protection would likely come about because the designers did a risk assessment, and found a hazard could occur (within the appliance itself) if the fault current was high.
 
Last edited:
The reality is this is a fixed load and so it would be perfectly safe without any overload protection and the existing 6.0mm supply cable would be adequately fault protected by the 32a device. But if manufacturer states a 16a device is required then that has to be taken into account.
 

Reply to Can i hardwire two 16amp aplliances into a hardwire point on a 6mm cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Can to OP clarify if this extension is just another room on the side of the building (so multiple cables going through the walls for lights...
Replies
6
Views
745
  • Question
yeah. i think so. Details here..... https://www.electriciansforums.net/threads/havent-seen-tel-for-a-month.210295/
Replies
14
Views
2K
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks