Some advise or views would be appreciated.

My supply is 100 amp single phase.

I purchased my property 3 years ago or so, the owner prior to the couple I purchased it from had installed a single external 32 amp socket near to the kitchen back door.

The cable to this socket is easy enough to trace, it runs externally from the 32amp socket in 25mm conduit vertically just over 2,5m into the property then under floorboards, ( no conduit ), where I can trace the cable to a 32amp MCB directly from the CU.

EDIT This socket is a blue 32amp socket.

The cable size is 6mm, the total cable run length from the socket to the CU is about 13m.

I now have to embark on learning a new skill, Mig Welding.

My front garden is 50m L x 26m W.

I have to do some running repairs and add to an existing metal palisade fencing some of which is at the furthest reach of the garden.

Having done some extensive reading and viewing I should think a simple 150 amp inverter Mig will do.

I have been able to get hold of 53mt of 3 Core HO7RNF 2.5mm² cable.

My intention is to attach a 32 amp plug to one end of the cable, a single 32 amp socket to the other end, remove any existing fused plug top attached to a new Mig and fit a 32 amp plug instead.

Will I be able to use a 150 amp rated Mig off the existing 32 amp socket in conjunction with the 50 odd metres of 3 Core HO7RNF 2.5mm² cable I have?
 
Last edited:
It is not permitted to have unshuttered socket outlets in a dwelling both 16 and 32A fall into this category.
If fitted with interlocks then no problem. It's also back to that classic argument of where does a 'dwelling' end - I've both 16 & 32's in my workshop, at home.
 
If fitted with interlocks then no problem. It's also back to that classic argument of where does a 'dwelling' end - I've both 16 & 32's in my workshop, at home.
My existing external 32amp socket will be replaced with one with RCD protection.

As @westward 10 says it is not permissible to fit an unshutterd socket in a dwelling, I didn't think it possible to buy an unshuttered version for domestic use for inside a property, I've never seen one.

Does the 16 or 32amp external type require an interlock switch?

I have no garage or work shed at the moment but working, using a very large, exposed concrete patio area.
 
If you are using a welder with 13A plug then a 13A extension lead is practical. You could make one with 2.5mm which is about as much that will squees in to decent 13A plugs & in-line sockets and a quick check says it is OK for VD at 40m length.

Or maybe better, put in a couple of fixed weatherproof sockets around the area so you are never more than 15m from one when you need it! That way 6mm cable could be used, but it has to be UV proof so not T&E !!! (Unless in conduit/trunking)
 
If you are using a welder with 13A plug then a 13A extension lead is practical. You could make one with 2.5mm which is about as much that will squees in to decent 13A plugs & in-line sockets and a quick check says it is OK for VD at 40m length.

Or maybe better, put in a couple of fixed weatherproof sockets around the area so you are never more than 15m from one when you need it! That way 6mm cable could be used, but it has to be UV proof so not T&E !!! (Unless in conduit/trunking)
In almost all other circumstances that would be a way forward but not in this instance, for me anyway.

I sought further advice from others and there seems to be a consensus.

As the Mig will have very little use and that use spread over a couple of months while learning how to weld before getting on in earnest and repairing and as the Mig will be used at the furthest end of the garden, (50m) for a short time only my intention is to do below.

Remove the 13a plug top supplied with the Mig and replace with a 16a plug.

Make up 50m of 3 Core HO7RNF 2.5mm² as an extension cable with 16a socket and plug at either end.

Replace the existing mounted 16a external socket with one that has RCD protection.

Incidentally both people I spoke to independently were appalled the original installer of the 16a socket relied solely on a 32a MCB for any kind of personal protection and why they didn't fit a RCBO, I'm grateful you mentioned the RCD.

They did say just for now stick to the 32a mcb but when done with all welding to swap it for a 16a mcb.

The 6mm cable that supplies the 16a socket from the CU would have been better run in 10mm but for my temporary welding needs "should" be ok.

Fortunately most of the welding repairs and metal fence add ons will be within a 25m radius of the 16a socket, still a long extension cable but better by half.
 
2.5 is beyond the specification for a 13A plug.
It is, I have in the past been guilty of squeezing 2.5 cable in to a plug top but not clever.

Repeating what I have been told and how I understood, manufactures of most electrical items they sell in the UK must fit a plug.

Clearly with items such as Mig welders they wish they hadn't to but UK law obliges them.
 
Incidentally both people I spoke to independently were appalled the original installer of the 16a socket relied solely on a 32a MCB for any kind of personal protection and why they didn't fit a RCBO, I'm grateful you mentioned the RCD.

They did say just for now stick to the 32a mcb but when done with all welding to swap it for a 16a mcb.

Were either of the people you sought alternative views from an electrician?

The reason I ask is it seems highly unlikely they'd be appalled by the original installation's lack of RCD protection, then advise that you go ahead and use the socket with overcurrent protection at twice its rating.

I don't mean to cause offence but, given that you're now pretty much at the plan originally posted, it seems as though you've more interest in seeking affirmation of your own ideas than sound advice.
 
Were either of the people you sought alternative views from an electrician?

The reason I ask is it seems highly unlikely they'd be appalled by the original installation's lack of RCD protection, then advise that you go ahead and use the socket with overcurrent protection at twice its rating.

I don't mean to cause offence but, given that you're now pretty much at the plan originally posted, it seems as though you've more interest in seeking affirmation of your own ideas than sound advice.
Yes both of them.

The advice, opinion for RCD protection for the 16A socket came from this thread and I mentioned it to both electricians, they didn't say not to, both agreed it a must.

Not seems, I am still seeking sound advise, opinions, further affirmation, are you saying I was told wrong and why?
 
Last edited:
I thought the regulation said they must not be used for household purposes, not that they cannot be installed in a dwelling or domestic installation?
[ElectriciansForums.net] Mig welding and cable run.
 
Exactly, household and similar use.

A welder requiring a 32A supply isn't household use regardless of whether it's a domestic installation.
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that the definition of ‘dwelling’ was the area served by the designated earthing system. On that basis my house has 16, 32 and (1ph > 3) 63/3 outlets for everyday household use - so I call BS on the whole thing!
 

Reply to Mig welding and cable run. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Can to OP clarify if this extension is just another room on the side of the building (so multiple cables going through the walls for lights...
Replies
6
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top