Calculate the appropriate size of the protective conductor exam question | on ElectriciansForums

Discuss Calculate the appropriate size of the protective conductor exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Joined
Nov 9, 2023
Messages
15
Reaction score
3
Location
Birmingham
fault = 400 A
Operating time of protective conductor = 0.15 s
Constant k, for the material of the conductor = 134

a 1.5mm
b 2.5mm
c 4.0mm
d 6.0mm

Just want to make sure I've got this right,
 
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
 
Upvote 0
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
Thank you so much for your help 👍🏻 much appreciated 🙂
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
thank you so much for your help, much appreciated 👍🏻🙂
 
Upvote 0

Reply to Calculate the appropriate size of the protective conductor exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

The cable needs protecting the same as if a load was connected on the far end of it, rather than a generator, except that it must not share a RCD...
Replies
7
Views
2K
While you can use the current/time plots for I2t, for the "instant" part of a MCB they are not really usable. MCB (and some MCCB) are...
Replies
4
Views
3K
Hi sorry, got major pc issues, (GPU faulty) Yes i have worked out both questions now sorry for late reply, Q1 GN3 page 51, Q2 i think have...
Replies
24
Views
5K
Yes, seen this before too - a pertinent reminder to look twice and not assume that something actually is what it obviously should be...!
Replies
7
Views
2K
In answer to another Peterborough colleague. Because we are all experienced practitioners, there is always a tendency to over think these multi...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks