fault = 400 A
Operating time of protective conductor = 0.15 s
Constant k, for the material of the conductor = 134

a 1.5mm
b 2.5mm
c 4.0mm
d 6.0mm

Just want to make sure I've got this right,
 
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
 
Upvote 0
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
Thank you so much for your help 👍🏻 much appreciated 🙂
These are often difficult questions, because although your calculation is correct - leading to the answer 1.5mm^2 there are sometimes related regulations.

So if the question relates to final circuits etc (I.e. twin & earth or whatever), this would be correct.

However, if the question relates to other areas, there are minimum conductor sizes - depending upon if the conductor is protected or not.

On face value, I would assume 1.5mm^2

Examiners tend to have a specific situation in mind when they write questions, which often isn't clearly presented
thank you so much for your help, much appreciated 👍🏻🙂
 
Upvote 0

Reply to Calculate the appropriate size of the protective conductor exam question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top