Just curious, has anybody else dealt with this?
16a Hager RCBO exceeding well above it's rating and for a long period of time.
 

Attachments

  • [ElectriciansForums.net] RCBO not tripping from over-current
    PXL_20240214_024843158.MP.jpg
    374.8 KB · Views: 53
  • [ElectriciansForums.net] RCBO not tripping from over-current
    PXL_20240214_024634129.MP.jpg
    318.4 KB · Views: 51
If you look at the trip time/prospective current graph (Fig 3A4 on page 370 of the big blue book - assuming it's a 60898/61009 compliant device with a Type B curve), at 20A that device probably won't ever trip until it gets tired from years of running at it's maximum capacity.
 
I’ve had experience of old mcbs getting stuck on after being pushed even near their limit to the point that a 16A could carry even twice that at times.
You could flick the switch off and the contacts inside remained closed.

Does your RCBO switch on and off as normal, ( and does the switch feel “soft” compared to others?) And does the test button work on it ok?

What is causing the overcurrent? Can equipment be removed from the circuit, or can the circuit design allow the RCBO to be replaced with a 20A version?
 
If you look at the trip time/prospective current graph (Fig 3A4 on page 370 of the big blue book - assuming it's a 60898/61009 compliant device with a Type B curve), at 20A that device probably won't ever trip until it gets tired from years of running at it's maximum capacity.
The hager graph for B curves gives an upper and lower limit. This overcurrent sits in the middle of those lines as they dissapear off the top of the graph, so it may or may not trip eventually
 
I’ve had experience of old mcbs getting stuck on after being pushed even near their limit to the point that a 16A could carry even twice that at times.
You could flick the switch off and the contacts inside remained closed.

Does your RCBO switch on and off as normal, ( and does the switch feel “soft” compared to others?) And does the test button work on it ok?

What is causing the overcurrent? Can equipment be removed from the circuit, or can the circuit design allow the RCBO to be replaced with a 20A version?
Yeah, I thought it might have seized inside, as it was only noticed after the storms here in Victoria. I was thinking of a possible surge may have damaged the mechanics inside the RCBO, but after changing it over for a new Hager RCBO, the issue is still there.

Prior to this, I had even plugged the two 10amp heaters (which were plugged into a single 10a double gpo) on another circuit to see if it would trip, with no success. We even had an older sparky come out and have a look at what he thinks and he didn't batt an eye, however a few other mates who are sparkys say the same thing I said, "it should have tripped".

The circuit normally has a printer on it, which barely draws anything, but one of the office staff plugged a couple of heaters in to dry up the carpet as it flooded the night prior. Upon walking into the office, I made this discovery and looked into why it wasn't tripping. These heaters had been running for roughly 4hrs.

I'm starting to think the Hager brand might just have a much higher tolerance, but kinda defeats the purpose.
 
If you look at the trip time/prospective current graph (Fig 3A4 on page 370 of the big blue book - assuming it's a 60898/61009 compliant device with a Type B curve), at 20A that device probably won't ever trip until it gets tired from years of running at it's maximum capacity.
That's crazy. I didn't have a load tester, but I'm questioning at what point will this RCBO actually trip. I only saw it at 21a, but depending on your derating factors, this is already in the area of not actually protecting the 2.5mm tps.
 
It will be rare but the piston through the overload tripping coil maybe subjected to contamination and stopping or slowing the piston moving as it should.
Yeah, I thought it might have seized inside, as it was only noticed after the storms here in Victoria. I was thinking of a possible surge may have damaged the mechanics inside the RCBO, but after changing it over for a new Hager RCBO, the issue is still there.

Prior to this, I had even plugged the two 10amp heaters (which were plugged into a single 10a double gpo) on another circuit to see if it would trip, with no success. We even had an older sparky come out and have a look at what he thinks and he didn't batt an eye, however a few other mates who are sparkys say the same thing I said, "it should have tripped".

The circuit normally has a printer on it, which barely draws anything, but one of the office staff plugged a couple of heaters in to dry up the carpet as it flooded the night prior. Upon walking into the office, I made this discovery and looked into why it wasn't tripping. These heaters had been running for roughly 4hrs.

I'm starting to think the Hager brand might just have a much higher tolerance, but kinda defeats the purpose.
 

Reply to RCBO not tripping from over-current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Random thought. Is there a smart meter nearby? Do we know of any cases of RCBOs affected?
2
Replies
26
Views
3K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
446
davesparks
D
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K
  • Question
It might be worth asking the customer to turn the oven on 45min before you arrive. then do an IR test on the oven from the isolator with the oven...
Replies
6
Views
1K
  • Question
Single Pole, Single Pole Switched Neutral, and Double Pole are all different things. Hager RCBO's are Single Pole. I was recommending Single Pole...
Replies
33
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks