The landlord should have had this done by now it is a legal requirement. I personally would not be touching anything until this is done. Can you show a picture of your consumer unit?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spur/Junction for outdoor socket for PHEV charging? in the DIY Electrical Advice area at ElectriciansForums.net
I fitted several of these GE boards back in the day. That's not a test button, it's an embossed section on the aluminium profile used to link the two SP switches that make up the main switch.Unless there is an rcd before that board ( looks like the main switch but has a little test button on it)
No RCDs in the house but there are two sockets outside on the rear conservatory that have RCD protection, assuming they’re safe to use?Unless there is an rcd before that board ( looks like the main switch but has a little test button on it)
It is unlikely to be suitable for the addition of an outside socket.
Was describing what an rcd looks like, NOT suggesting that the board had one!I fitted several of these GE boards back in the day. That's not a test button, it's an embossed section on the aluminium profile used to link the two SP switches that make up the main switch.
What about the outdoor RCD sockets on the conservatory?You have no sockets that are suitable for supplying anything outdoors. This includes the sockets inside the house.
Reply to Spur/Junction for outdoor socket for PHEV charging? in the DIY Electrical Advice area at ElectriciansForums.net