If you were to test a metal staircase on the side of the house on insulation resistance and it gave you a dead short. Would that need bonding. Test was done at the MET with all parallel paths disconnected. Staircase next to class 1 metal light fittings
 
Last edited:
[ElectriciansForums.net] Extraneous metal staircase
 
Great thanks for the advice. Am I right in thinking though, although not the best way to test...if the IR is below 0.0067Megaohms then it would certainly need bonding. My results were 0.000 Megaohms
0.02 MΩ, then the part in question is considered as unable to introduce a shock risk and, as such, won’t require bonding.
 

Reply to Extraneous metal staircase in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top