hi all,

What are your thoughts on how the 6231 cables been terminated? Will aluminium cause eddy currents? Thanks
 

Attachments

  • [ElectriciansForums.net] Eddy current clarification
    IMG_3857.png
    2 MB · Views: 104
  • [ElectriciansForums.net] Eddy current clarification
    94BE07C3-3A22-4AC2-AAC2-C94A3D88BD5A.jpeg
    302.2 KB · Views: 62
There might be some eddy current effects but far less than for steel (or anything other exotic material that is ferromagnetic). See 521.5.1 for that.

Ideally you always would take the whole set through a single hole, it also helps preserve circuits when several are present so less connection errors (i.e. L1-3, N & E kept to same MCB, etc, etc) than if they are going via different holes.
 
Seems I am mistaken - thanks 🫣
You are not mistaken, eddy currents (Foucault currents) will be induced in any conductor within the presence of a changing magnetic field.

However the ferrous material tends to enhance the effect.

I have to say though, we designed MV and HV switchgear for typical currents of circ 630 - 3000 A and using 1/4" steel plate we used separate apertures for each phase, and only added around 5-10 deg C temperature rise!

So in my opinion it doesn't matter at all whether the cables go through the same hole or different holes.

However if it is ferrous material, regulation 521.5.1 mandates that all current carrying conductors go through the same hole.
 
I have to say though, we designed MV and HV switchgear for typical currents of circ 630 - 3000 A and using 1/4" steel plate we used separate apertures for each phase, and only added around 5-10 deg C temperature rise!

This is interesting, but I believe the eddy current problems get worse the thicker the steel gets.

The eddy currents become an issue if the conductors don't just pass through separate holes but also separate couplers or even conduits.

I've been meaning to experiment with this for a while, maybe I'll get some time in the workshop soon.
 

Reply to Eddy current clarification in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Yes that is correct
Replies
1
Views
1K
Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
317

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top