Bengaz

-
Joined
Jan 2, 2013
Messages
16
Reaction score
0
Location
South Shields
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth electrode to each unit. Did anyone know that? The NICEIC tech help didnt today...

Even though NPG supply a MET cant be used.

A break in the neutral supplying any unit and the current would flow through the frame and back to the transformer via the PME link in an adjacent unit. You may never know there was an external fault.
 

Attachments

  • [ElectriciansForums.net] Steel framed units multiple PME supplies
    WhatsApp Image 2024-02-27 at 19.25.05_c8b37768.jpg
    238.6 KB · Views: 19
Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth electrode to each unit. Did anyone know that?

Yes, this is standard practice with all DNO's, I think may even be derived from ESQCR or something like that.


The NICEIC tech help didnt today..

Say no more.

.A break in the neutral supplying any unit and the current would flow through the frame and back to the transformer via the PME link in an adjacent unit. You may never know there was an external fault.

It's worse than that, the normal neutral currents of each installation will be diverted via the steel structure of the building via the bonding and back through the other supplies
This means you'll have current constantly flowing through the steel structure which can lead to all sorts of issues, possibly including accelerated corrosion of the steelwork
 
Thank you, I had not considered the higher current in the good PEN, I must look as the building I work in has 3 or 4 supplies, there were separate units, but now are all combined and the cost of having supplies removed exceeds the cost of the standing change by a huge amount, so they were left in, although lightly used.

I was told it was PME and that the EV charge point has it's own earth rod, but never really looked as had no need to.
 

Reply to Steel framed units multiple PME supplies in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

  • Question
No, that is part of a different earthing system, don't mix the different earthing systems unless you have given proper engineering consideration...
2
Replies
27
Views
3K
davesparks
D
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top