Multiple commercial units within the same steel frame cant each have a PME supply (from the same transformer), we have to install an earth electrode to each unit. Did anyone know that? The NICEIC tech help didnt today...
Even though NPG supply a MET cant be used.
A break in the neutral supplying any unit and the current would flow through the frame and back to the transformer via the PME link in an adjacent unit. You may never know there was an external fault.