spd in meter box? | on ElectriciansForums

Discuss spd in meter box? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 9, 2021
Messages
1
Reaction score
0
Location
pembs
Client needs an SPD fitting but no room in c/u or adjacent. Best bet looks like a parallel connection into the tail blocks in the meter cabinet with an adjacent 'standalone unit' ie with overcurrent protection. Anybody done this? Any reason I shouldn't? Is it ok to use board PEN connection block for earth?
 
Wylex do a tail isolator with type 2 SPD that's rated at 100A so no need to fuse down. This is what I would use just make sure you get your supply and load around the right way round.
[ElectriciansForums.net] spd in meter box?
 

Same idea but 1/4 the price...! Have fitted both and not a huge difference in quality tbh , Wylex obvs the benchmark though but I'll be mostly fitting the WCED ..
 

Reply to spd in meter box? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top