Hi. As part of safe isolation we use a voltage tester to prove dead; I've been taught that this is done by putting the probes in the following combinations: N+L, N+E, E+L.

But why check anything apart from the Live? That's where the voltage is coming from right?
 
Hi. As part of safe isolation we use a voltage tester to prove dead; I've been taught that this is done by putting the probes in the following combinations: N+L, N+E, E+L.

But why check anything apart from the Live? That's where the voltage is coming from right?

How would you check just the L ?
How would you know that the N is disconnected
How would you know that the E isn't L
 
This sounds good but I don't really understand. Can you point me to a resource with a fuller explanation please? I have spent most of the evening looking online but just can't find it
What is the part that you can't understand ?

This explains a bit.
 
What is the part that you can't understand ?

This explains a bit.
Thanks for this, fortunately I am familiar with the process itself but what I am stuck on is if we need to check that there is no voltage potential in each conductor why a tester couldn't be designed that you simply put on the end of the conductor (like a voltage pen but I understand they are not considered reliable enough)? So in your explanation above I don't understand "without a reference".
 
Thanks for this, fortunately I am familiar with the process itself but what I am stuck on is if we need to check that there is no voltage potential in each conductor why a tester couldn't be designed that you simply put on the end of the conductor (like a voltage pen but I understand they are not considered reliable enough)? So in your explanation above I don't understand "without a reference".
When you do a voltage test the test instrument is checking is there a "pressure" difference between that point and another point. When it is testing the pressure difference a very tiny current has to "flow" in the test instrument. To allow the test current to flow it is a two pole device and thus needs two connections. This is also why you need to be able to prove the tester works before and after any proving dead tests, this needs either a proving device or a known live that is still live such as the supply side of the main switch.
 
I think there are two concepts here...
1 - the measurement of electricity - an alternative term for voltage is "potential difference" and I think it will help you to think of it like that. Any time we measure voltage we are measuring between two things. Any other method is unreliable and pretty meaningless as you can't say with confidence what it will do to you by just touching one point.

2 - how the electricity is made. the best diagram I can find at this time of night is this one which I've added to a bit...

The mass of earth is used by the supply companies as a reference voltage of 0v, and in simplified terms "neutral" is earthed to keep it as close to earth as possible, at least once at the transfomer, often more times.

[ElectriciansForums.net] Voltage testers - a basic question


Taking into account how we must measure between two things, on a single phase system we are measuring between the phase peaks and the horizontal axis of the graph, which in this simplified example is the other end of the coil.
(When you come to test 3 phase systems, you will test between phases, and are measuring from the top of one peak to the bottom of a different coloured line, and that is why you get a bigger potential difference, around 400v.)

I don't know if I'm helping or confusing you more, so I'll stop now.
 
To put it in laymans terms a voltage test is always telling you the voltage difference between two points. A live wire is only live because its voltage is 230v different to the actual ground you're standing on or to the neutral that is usually connected to the ground you're standing on. In normal circumstances if you test between live and neutral or live and earth the tester will indicate or display this 230 volt difference.

The problem comes when there's a fault such as a neutral wire that's no longer actually connected to the neutral of the supply anymore. That neutral wire is no longer held or clamped at zero volts, it would be floating at any voltage that's applied to it so when you put your tester between the live and neutral there's an electrical path through your tester (allbeit a high resistance one) that will connect the 230 volt potential (voltage) of the live to the neutral that is floating causing the neutral wire to also become 230v. The difference in voltage beyween the 230v live wire and the now 230v neutral wire is zero and that's what the tester will display even though the live wire will injure or kill you if you touch it.

Likewise if the cpc (earth wire) isn't connected to anything it will also give you false readings on your tester when proving dead same as the broken neutral did. The reason you do 3 different tests is to reduce the possibility that the circuit you're testing could have a faulty conductor that will give you false reading during a safe isolation test that could kill you.
 
In simplest terms, a DC battery has two connections. Out one end, to a load (light) back to the other end to creat a circuit.

AC circuits are exactly the same. Out on the live, through a load, back on the neutral. Live and neutral are just the words we use to name the two wires going back to the source. Power station etc.

We added an earth cable as a safety feature. And as mentioned, the earth and neutral are connected at several places.
If we test N-E, and there is a marked voltage present where we know there shouldn’t be, then we can assume there is a fault.
 
Some very good answers now! I guess you can think of a 2 pole tester as internally saying “if I look for a source of electricity on one pole and and a return path on the other pole, is there enough to do anything with it in the middle”
It tests how the electricity will behave in real life.
A good 2 pole tester will in fact alert you to a supply and no return path but this can’t be relied upon, not least because an internal battery is needed for this test. (Even if the battery is missing or discharged, a 2 pole test will still work.)
 
Ok but still, why test between 2 conductors? Why not test each individually?
As a few others have already said, what you measure is voltage difference. The good example from above is a battery, it will do nothing unless you have contact to both terminals.

But as with many things, you can define a point to be something, and measure relative to that to have some absolute (rather than relative) measure. For electrical power we define the Earth (i.e. our planet) as being at 0V and then we can reference anything with respect to that arbitrary point. A Martian might find our planet is at a different potential to Mars, but we don't care as all we are doing is working here on Earth.

Now the difference between a battery and the AC power system is that in almost all cases, we take one of the live conductors (i.e. those carrying current) and reference it to the Earth through some conductive path, usually an earth rod or mat at the generator or substation. The live conductor we chose to reference to E we call neutral as normally it has very little voltage on it, all of the others we call line and for the typical UK system we have a nominal 230V L-N and 400V L-L (the physical diagram of the generator in post #10 helps explain the 1.73 ratio).

When you are "proving dead" you absolutely must not assume anything about the wires in front of you. They may not have been connected/colour-coded correctly and/or they may be subject to a fault, and if you make a mistake it will be a doctor proving you are dead!

This is why you must follow the correct procedure for proving dead before any work, and you will automatically fail any practical exam if you don't. So you check from each conductor to every other conductor (and maybe to any metal work if the CPC is not already connected to it) to see if any combination could prove dangerous, not just the L you might expect. If you have a total of X conductors you have X*(X-1)/2 combinations to check, which works out as 3 for single phase (L+N+E) and 10 for most three-phase (3L+N+E) systems.

You can get no-contact voltage indicators which work by looking for electrical fields around the conductor. While these have some uses, they are not acceptable for proving dead as there can be situations when they do not reliably indicate voltage differences, and other cases when they incorrectly show a live conductor due to capacitive coupling from another cable ("phantom voltage"), a problem you also get with digital multi-meters due to their high impedance (hence very little current needed to register a voltage).
 
I always do a live test before to ensure that there actually is an L N E.
That's also the way I do it, I prove the integrity of the circuit first before proving the state of the supply on it but I didn't want to suggest it in case that's not the way they teach it nowadays.
 
Generally taught earth to line, keep probe on earth then earth to neutral then keep probe on neutral and neutral to line. Same principle for single or three phase. You wouldn't be criticised if you didn't do this providing all sequences are done but getting a method in your head will help. It is acceptable to use the last test, line to neutral to verify operation of the instrument but tell your tutor.
 
When asked a similar question I always refer to this John Ward video:
View: https://www.youtube.com/watch?v=-qh28sHs7XA


If you are not at the CU, a proving unit is essential.
Why some folks baulk at the price is a mystery to me...die and leave partner and kids behind?

OK, we all do the plug-in tester, switch the mcb or rcbo off, wave a non-contact tester over the socket or whatever, and carry on...but proper testing, test the 2 pole tester before, do the test, test it again...it just makes sense.
Also good advice...do not take anyone else's word that a circuit is dead...always do your own checks.
 
Also good advice...do not take anyone else's word that a circuit is dead...always do your own checks.
Good advice,
not doing the above has cost me a pair of nearly new cutters in the past, cant remember if a new pair of underpants was required but it is an altogether unpleasant experience (at best) and of course in some cases it may be fatal.

trust me, the flash and bang not only tells you that you have messed up but also anyone who is near. it will cause any customer you may have to be somewhat concerned about your level of competence as an electrician.

therefore if you are lucky enough to come away with no physical injury, you are more than likely going to get some sort of financial penalty as people no longer see you as a professional.
 
THANK YOU one and all.

I do struggle with the theory side of my learning as science has never come naturally to me, but I feel I understand this one now so I'm very grateful, cheers.
One thing that maybe is worth a mention is to always put the probe on E or N first as depending on the impedance of the instrument, once you connect the probe to L the other end of the probe will become L If you are touching earth and touch the N probe at the same time you can get a shock.
 
Last edited:

Reply to Voltage testers - a basic question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K
  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
532
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K
  • Question
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
1K
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks