Thanks @loz2754.
Out of academic interest, you are right about the reason. Having just read the 16th edition equivalent section it's basically the result of simplifying many very complicated regs about EEBADS, protection from indirect contact to exposed conductive parts, and requiring reduced disconnection times. (Interestingly distribution circuits were in fact excepted back then).
Requiring absolutely everything to be RCD protected in this context makes a little more sense.
--
The thing now occupying my brain is "what if D was fenced off".
The supply circuit and circuits to house and camp site become out of scope.
But the distribution circuits going into the field serving points in the field still need 300ma RCD protection.
In some ways sticking a 300ma RCD at source of it all would put this issue to bed, but would also mess up loop testing for evermore for lots of things! I'm there again tomorrow and will have a think.
Out of academic interest, you are right about the reason. Having just read the 16th edition equivalent section it's basically the result of simplifying many very complicated regs about EEBADS, protection from indirect contact to exposed conductive parts, and requiring reduced disconnection times. (Interestingly distribution circuits were in fact excepted back then).
Requiring absolutely everything to be RCD protected in this context makes a little more sense.
--
The thing now occupying my brain is "what if D was fenced off".
The supply circuit and circuits to house and camp site become out of scope.
But the distribution circuits going into the field serving points in the field still need 300ma RCD protection.
In some ways sticking a 300ma RCD at source of it all would put this issue to bed, but would also mess up loop testing for evermore for lots of things! I'm there again tomorrow and will have a think.