Writing up a sizable EICR, one circuit is utilizing FP200 type cable (don't know the exact brand sorry I know they differ) for a 3 phase condenser, but the only ratings I can find for any softskin cables state single phase AC.

Is 3ph AC even permissable?
 
What you need to look at is the voltage rating of the cable and at a minimum it is likely to be 300/500v so this is fine. If the cores are contained within one cable this is also fine. If the cable is exposed to sunlight this probably isn't fine.
 
Oh, I was under the impression fp had different ratings, think I was confusing it with that "refer to manufacturer" SY stuff, thanks

All I need now is zs for MG 60947-2s, which you think would be easily accessible info wouldn't you



Includes Zs for MG 60947s

Unfortunately it's £10.
 
Oh, I was under the impression fp had different ratings, think I was confusing it with that "refer to manufacturer" SY stuff, thanks

All I need now is zs for MG 60947-2s, which you think would be easily accessible info wouldn't you

All of the information for MG stuff is freely available from Schneider
 

Reply to FP200 3 phase rating? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
522
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
469

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
266

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top