Fault finding job | on ElectriciansForums

Discuss Fault finding job in the Commercial Electrical Advice area at ElectriciansForums.net

Joined
Dec 2, 2021
Messages
72
Reaction score
36
Location
Wales
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this morning to test and was told that her cooker was tripping the rcd.
Before checking the cooker element I did an rcd test this morning on the left side of board (side with cooker circuit) and the rcd wouldn't trip. Did an rcd test on the right rcd and it would trip both rcds. Would touch neutral to earth on the cooker circuit and nothing would trip.
Anyway the fault was that a neutral was touching the outer casing of a light (see photo) that makes sense about the rcd tests, because the fault current the rcd sends out will go through the earth and back up the neutral cable of the lights and make its way back to the rcd.
I am a bit confused though on why this neutral to earth fault didn't just immediately trip the rcd? Am I right in thinking that it's probably due to the highish ze of the TT rod? So the fault current just wants to flow through the neutral as appose to the earth and it would only trip with the cooker because enough current is drawn therefore more fault current and more current going through the earth as well as the neutral

[ElectriciansForums.net] Fault finding job
 

Reply to Fault finding job in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
663

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top