Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this morning to test and was told that her cooker was tripping the rcd.
Before checking the cooker element I did an rcd test this morning on the left side of board (side with cooker circuit) and the rcd wouldn't trip. Did an rcd test on the right rcd and it would trip both rcds. Would touch neutral to earth on the cooker circuit and nothing would trip.
Anyway the fault was that a neutral was touching the outer casing of a light (see photo) that makes sense about the rcd tests, because the fault current the rcd sends out will go through the earth and back up the neutral cable of the lights and make its way back to the rcd.
I am a bit confused though on why this neutral to earth fault didn't just immediately trip the rcd? Am I right in thinking that it's probably due to the highish ze of the TT rod? So the fault current just wants to flow through the neutral as appose to the earth and it would only trip with the cooker because enough current is drawn therefore more fault current and more current going through the earth as well as the neutral

[ElectriciansForums.net] Fault finding job
 

Reply to Fault finding job in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
551
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
660
  • Question
I misread it.
    • Like
Replies
13
Views
828
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
683
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
440
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks