Bear with me because this is long. So got an intermittent fault on the upstairs lights. Trips the mcb after a few hours, getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth, so I think the cable is obviously damaged but can’t understand why this isn’t showing when I test and why it’s tripping intermittently. Maybe I’m missing something completely obvious
 
What does L-E measure at the board when using a low Ohms test rather than an IR test?
 
Bear with me because this is long. So got an intermittent fault on the upstairs lights. Trips the mcb after a few hours, getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth, so I think the cable is obviously damaged but can’t understand why this isn’t showing when I test and why it’s tripping intermittently. Maybe I’m missing something completely obvious
Have you meggered both sides of first leg leaving db going to first switch.could be damaged on one side maybe does your first feed connect onto any strappers if its up stairs lights
 
Bear with me because this is long. So got an intermittent fault on the upstairs lights. Trips the mcb after a few hours, getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth, so I think the cable is obviously damaged but can’t understand why this isn’t showing when I test and why it’s tripping intermittently. Maybe I’m missing something completely obvious
I always have a diagram written out of how I wired the lighting circuit. If you have one, pop it up. It'll make it easier to see where you are testing in the circuit.
Are your conductors removed from the mcb AND neutral bar (in the CU) when you are testing?
Is it definitely an MCB not an RCBO?

I think you must be missing something simple, as the 0.01 cannot disappear. You will find it, and think.. 'oh, that's so obvious'.

It will be something to do with the break in the earth. The initial test (0.01Mohms) is including the fault.

The next 2 tests somehow bypass the fault. Are you sure the fault is not on another circuit, again this could be getting picked up through the L, if you have left the neutral connected in the neutral bar. There could be a neutral earth fault on another circuit (or L-E). This may explain the poor result, but not the tripping.

Good luck chap. Go back the next day, in the morning. I have found so many faults within a few minutes the following morning after looking for hours the previous afternoon, as I have a fresh head. Plus a bit of help from here most likely.
 
Last edited:
Have you meggered both sides of first leg leaving db going to first switch.could be damaged on one side maybe does your first feed connect onto any strappers if its up stairs lights
Disconnected feeds at first switch, fault disappears when I do this. But when I test the outgoing feed I get 5.2 megaohms or something. When I reconnect this out going feed the 0.01 reading re appears at the consumer unit again
 
Bear with me because this is long. So got an intermittent fault on the upstairs lights. Trips the mcb after a few hours, getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth, so I think the cable is obviously damaged but can’t understand why this isn’t showing when I test and why it’s tripping intermittently. Maybe I’m missing something

Bear with me because this is long. So got an intermittent fault on the upstairs lights. Trips the mcb after a few hours, getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth, so I think the cable is obviously damaged but can’t understand why this isn’t showing when I test and why it’s tripping intermittently. Maybe I’m missing something completely obvious
You could perform your continuity tests again on lighting legs again but individually
 
I always have a diagram written out of how I wired the lighting circuit. If you have one, pop it up. It'll make it easier to see where you are testing in the circuit.
Are your conductors removed from the mcb AND neutral bar (in the CU) when you are testing?
Is it definitely an MCB not an RCBO?

I think you must be missing something simple, as the 0.01 cannot disappear. You will find it, and think.. 'oh, that's so obvious'.

It will be something to do with the break in the earth. The initial test (0.01Mohms) is including the fault.

The next 2 tests somehow bypass the fault. Are you sure the fault is not on another circuit, again this could be getting picked up through the L, if you have left the neutral connected in the neutral bar. There could be a neutral earth fault on another circuit (or L-E). This may explain the poor result, but not the tripping.

Good luck chap. Go back the next day, in the morning. I have found so many faults within a few minutes the following morning after looking for hours the previous afternoon, as I have a fresh head. Plus a bit of help from here most likely.
So i basically go from the board to upstairs hall. From the hall to bed room 1, from there to the bathroom then finishes at bedroom 2. Between hall and bedroom 1 I lose the earth in the cable somehow, possible compression or joiner screw through it. But lights all work fine so live and neutral haven’t been broken. 0.01 ohms when I test between live and earth at db, this reading disappears when I disconnect feeds at hall switch. But when I test outgoing feed at hall switch I don’t get a reading of 0.01 megaohms I get 5.2. Tested strappers and all clear. It’s a head scratcher lol
 
1056 ohms I got im sure
That would be 0.001Mohms not 0.01Mohms. Give us some accurate figures and don't guess. If you don't know, just say you don't know. This is said because facts are required, no offence is meant.
 
So i basically go from the board to upstairs hall. From the hall to bed room 1, from there to the bathroom then finishes at bedroom 2. Between hall and bedroom 1 I lose the earth in the cable somehow, possible compression or joiner screw through it. But lights all work fine so live and neutral haven’t been broken. 0.01 ohms when I test between live and earth at db, this reading disappears when I disconnect feeds at hall switch. But when I test outgoing feed at hall switch I don’t get a reading of 0.01 megaohms I get 5.2. Tested strappers and all clear. It’s a head scratcher lol
A diagram speaks a thousand words. We can't tell if you're looping at the switch, or the lights or both, or if there are 2 way switches, or more than one light per switch.

Hopefully you'll find it tomorrow, but if not then take the time to draw out the circuit and pop it on here.
 
getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth
Possibly:

Your IR tests carried out downstream of the first switch are between line and the floating CPC, that is not connected to the earthing system.

However, the fault may not be between line and that floating CPC. It may actually be between line and some other part of the building that does have a tenuous connection to the earthing system. Hence why you get low IR L-E tested at the board (where the CPC is connected to the MET), but not downstream of that first switch.

Try: Connect your wander lead to the MET, and take that with you to a point downstream of the first switch, and do your IR test between L and the wander lead. I suspect you will now get a low IR reading.

Had a similar fault yesterday. Low IR 0.08 N-E, but the CPC had become disconnected somewhere. Once the CPC was reconnected, it was a dead short of a fraction of an ohm.
 
That would be 0.001Mohms not 0.01Mohms. Give us some accurate figures and don't guess. If you don't know, just say you don't know. This is said because facts are required, no offence is meant.
No it’s not. He asked what reading I got when I tested on low resistance ohms so wasn’t megaohms. So maybe it’s yourself that needs to know the facts beforehand
 
Possibly:

Your IR tests carried out downstream of the first switch are between line and the floating CPC, that is not connected to the earthing system.

However, the fault may not be between line and that floating CPC. It may actually be between line and some other part of the building that does have a tenuous connection to the earthing system. Hence why you get low IR L-E tested at the board (where the CPC is connected to the MET), but not downstream of that first switch.

Try: Connect your wander lead to the MET, and take that with you to a point downstream of the first switch, and do your IR test between L and the wander lead. I suspect you will now get a low IR reading.

Had a similar fault yesterday. Low IR 0.08 N-E, but the CPC had become disconnected somewhere. Once the CPC was reconnected, it was a dead short of a fraction of an ohm.
I had the CPC disconnected at the consumer unit when I was testing the cable
 

Reply to Fault on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
455
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
747
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
747
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top