Bear with me because this is long. So got an intermittent fault on the upstairs lights. Trips the mcb after a few hours, getting a reading of 0.01 mega ohms between live and earth at the board, tested cable going to db from first switch and it’s clear. Tested the cable going from first switch to rest of switches and getting a reading of 5.2 megaohms so can’t understand where the 0.01 is coming from as I wired it so know there isn’t any joins. Also the cable going from first switch to rest of switches loses its earth, so I think the cable is obviously damaged but can’t understand why this isn’t showing when I test and why it’s tripping intermittently. Maybe I’m missing something completely obvious
Is there 2 faults here or if the cpc between db and first switch was clear between l,n,e and not damaged and earth continuity verified then cpc further down the line might be restored .or have I misunderstood your wiring description
 
Is there 2 faults here or if the cpc between db and first switch was clear between l,n,e and not damaged then cpc further down the line might be restored .or have I misunderstood your wiring description
So there is 2 faults but I don’t know if they are linked. Basically losing the CPC between switch 1 and 2. But not sure if this is what’s causing the tripping as the cable must be damaged
 
Possibly:

Your IR tests carried out downstream of the first switch are between line and the floating CPC, that is not connected to the earthing system.

However, the fault may not be between line and that floating CPC. It may actually be between line and some other part of the building that does have a tenuous connection to the earthing system. Hence why you get low IR L-E tested at the board (where the CPC is connected to the MET), but not downstream of that first switch.

Try: Connect your wander lead to the MET, and take that with you to a point downstream of the first switch, and do your IR test between L and the wander lead. I suspect you will now get a low IR reading.

Had a similar fault yesterday. Low IR 0.08 N-E, but the CPC had become disconnected somewhere. Once the CPC was reconnected, it was a dead short of a fraction of an ohm.
I will try this when I’m next on the job, thanks for the help.
 
No it’s not. He asked what reading I got when I tested on low resistance ohms so wasn’t megaohms. So maybe it’s yourself that needs to know the facts beforehand
Like I said, don't take offense.
I'm just speaking factually.
You said 'I think' I got, therefore I'm just asking for accurate figures.
It would be very surprising to get a reading almost exactly 100 times smaller than the IR reading. It's more likely that you got 10000 ohms.
 
Any electronics in circuit that might be skewing the readings?
Smokies. Or smart switches?

Might have been covered already, but what about shared neutrals from another circuit still connected to earth at source
 

Reply to the thread, titled "Fault on lighting circuit" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top