earth rod for TL invertors | on ElectriciansForums

Discuss earth rod for TL invertors in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

J

josh55

Iv been told you need to install a earth rod to earth array when using transformerless invertors ,seems a bit ott rcd not enough ?
 
Yes Josh apparently its true, (see the ‘array frame earthing decision tree’, in the DTI guide), but you only need to do this if it’s a PME supply. Use 10mm. Good luck
 
class a rcbos for pulsed dc for transformerless TL inverters to stop dc leaking into the grid
as these have no galvanic separation , HF range has transformers fitted but yields are lower
per esc guidelines i have supplied these for over two years now
also plug in grounding kits if hybrid sanyos or thin film panels are used
 
Yes Josh apparently its true, (see the ‘array frame earthing decision tree’, in the DTI guide), but you only need to do this if it’s a PME supply. Use 10mm. Good luck

Not strictly true. If PME then earth stake array in 10mm earth, If TNS or TT then earth bond array back to MET in this case the size of bond cable must be equal size to bonding conductors already installed to the water, oil, gas etc.
 
class a rcbos for pulsed dc for transformerless TL inverters to stop dc leaking into the grid
as these have no galvanic separation , HF range has transformers fitted but yields are lower
per esc guidelines i have supplied these for over two years now
also plug in grounding kits if hybrid sanyos or thin film panels are used

Its a Class B RCD not RCBO. RCBO's are not good practice to protect PV as most are not double pole. Regardless of this the Class B RCD is required to protect TL's from injecting DC into the AC system.

As for the Sanyo's I was told by Sanyo rep that grounding kits are not a requirement.
 
Not strictly true. If PME then earth stake array in 10mm earth, If TNS or TT then earth bond array back to MET in this case the size of bond cable must be equal size to bonding conductors already installed to the water, oil, gas etc.

Apologies Josh, missed that bit! Marc C is correct; if it’s PME then stake it and if not then take it back to the CET
 
sanyo hybrid mono and thin film
sanyo recommend grounding but not mandatory
if using transformerless inverters
okay with transformer inverters as they have galvanic isolation
thin film produces much higher voltage than mono or poly
sma and others make inverter grounding kits for sanyo and thin film modules
thin film over produces in voltage for first few weeks up to 12weeks until it settles down
also at low temperatures in strong sunlight as virtual junction temperature is low
esc guidelines recommend pulsed dc rcds/rcbos fitted to inverter outputs to stop dc feeding into the grid


can send data sheets if required
 
can email full sanyo data on grounding
not mandatory but recommended by sanyo
esc guidelines on transformless inverters recommend class a not class b rcds
 
esc guidelines on transformless inverters recommend class a not class b rcds

That's not what the version I have says.

Regards
Bruce

[ElectriciansForums.net] earth rod for TL invertors
 
so i see bruce this states as you say above
above/esc/bs7671 all different
pv regulations still need to be sorted out in the uk on lots of details
excludes 95% of your competitors with zero electrical knowledge who don,t fit anything at all
 

Reply to earth rod for TL invertors in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top