If the maximum power consumption of a machine is said to be 42kVA 3 phase, I worked it out to be around 58 amps. This total current must be over the 3 phases, or am i missing something.
 
If the maximum power consumption of a machine is said to be 42kVA 3 phase, I worked it out to be around 58 amps. This total current must be over the 3 phases, or am i missing something.

I got it to 60.62

I may be well of the mark here, could some one please advise me where I've got wrong, If I have.

I did, 42000 / 692.8 (1.732/400)
 
Last edited by a moderator:
malcolm, i have to disagree with you here.

42KW is 14kw/phase

I=14000/230=60.86. ( not allowing for power factor.)
 
Cheers guys,

so how come then this machine is happily running day in day out sat on a 32 a c type breaker.

love the quiet days sat at home, it makes up for the days i didn't bother listening at college:freak:
 
either the MCB has a good overload tolerance, or could be it's contacts are welded together. what size is the cable feeding the motor?
 
4mm 4 core SWA. Been installed for almost 8 years and doesn't show any signs of overheating anywhere.

Going to go in armed with my clamp meter anyway to check it out
 
Malc, this is what i'm thinking. I'm not the brightest spark, but even i thought that lol

I'll find the spec page for the machine and post it
 

Reply to Current rating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
753

Similar threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
648
Thank you, Both are heat / cool only.
Replies
3
Views
577

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top