Well the the Axis is 5.5 kw and there is a spindle that is 7.5Kw so there is the 13Kw of power and that is over the 3 phases 13kw/ 1.732 x 400 = 18.8amps per phase
Forget the PF and any lagging efficiency for this calc.
Well the the Axis is 5.5 kw and there is a spindle that is 7.5Kw so there is the 13Kw of power and that is over the 3 phases 13kw/ 1.732 x 400 = 18.8amps per phase
Forget the PF and any lagging efficiency for this calc.